Anonymous Poster

Safe Location of Fired Heater in a Oil Terminal

04/12/2010 7:14 AM

Please let me know what is the safe distance that need to be maintained from class I and Class II product storage tank to the hot oil system used to heat fuel oil tanks. I had refered to NFPA 30, 31 etc,. to find, still i am not sucessful. I need this data to decide the plot plan of the oil terminal.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Piping Design Engineering - Retired Piper

Join Date: Feb 2007
Location: Bayonet Point, Florida
Posts: 635
Good Answers: 61
#1

Re: Safe Location of Fired Heater in a Oil Terminal

04/12/2010 11:48 AM

I think it depends on whether the "Heater" if fired or steam heated.

If you have a Flame Fired Heater involved then it should be located up wind and a minimum of 60 meters away from any source of flammable vapors.

If no flame involved then it does not mater where you located it. However, I would locate the heater outside of the dike (spill retention area).