i want technical specification for a 2MVA, 6.6/.433 KV transformer

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Transformer spec

04/13/2010 11:13 AM

DESCRIPTION: power transformer
POWER RATING: 2 MVA
PRIMARY VOLTAGE: 6.6 KV
SECONDARY VOLTAGE: 0.433 KV

Reply
Participant

Join Date: Oct 2009
Location: JAMSHEDPUR, INDIA
Posts: 3
#2

Re: Transformer spec

04/13/2010 11:38 AM

2 MVA

PRIMARY VOLTAGE - 6.6 KV , COOLING - ONAN/ONAF

CURRENT-175 A , IMPIDENCE VOLTAGE -8.55 %

SECONDRY VOLTAGE - 433 V

CURRENT- 2666 A

CONNECTION - DYN11

Reply Off Topic (Score 6)
Anonymous Poster
#3

Re: Transformer Spec

04/14/2010 9:39 AM

kVA = 2000

f = 50Hz

Voltage ratio = 6600 / 433 V

Connection = Dyn-11

%Z = 6%

Taps = +5 , +2.5, -2.5, -5, -7.5

Temperature Rise = 55 / 65 C

Fe Losses = 2.2kW

Cu Losses = 24.5kW