Generator Supply Volt Drop Problem

04/15/2010 10:53 AM

Hı Folks,

Searched the forum but could not find a similar problem surprisingly. We are planning to have a 630kva 3 phase generator supplying a load around 150m away - not ideal I know. The calculations to comply with 4% volt drop are resulting in about 12 x 240mm cables per phase - not very practical! I have installed transition boxes for this amount of cables on gensets before but is there any other way of overcoming the volt drop issue ? Generating voltage at a higher lever ? installing compensations panels inline ? I'd appreciate the Experts' views.

regards

GC

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Generator supply volt drop problem

04/15/2010 11:34 AM

Using 480 volts and 500 mcm(253mm) cu I calculated 1.28% with 2 conductors per phase. Total load 760 amps. You did not list the voltage.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Jan 2010
Posts: 2446
Good Answers: 60
#2

Re: Generator supply volt drop problem

04/15/2010 1:08 PM

there is a thread on here like that but you will have to search this lot.

http://cr4.globalspec.com/forum/electrical-engineering

or use the search window on the right as has already been sugested

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Generator supply volt drop problem

04/15/2010 1:56 PM

The easiest way to keep the voltage drop within the limit is to

(1) use the larger size of the cable or

(2) increase the number of cable (parallel cables of same size) or

(3) Both (use larger size of multiple cables of same size)

Do the voltage drop calculation for the option you select and make sure the voltage drop is within the specified limit. For option 2 and 3, current will be equally divided between the cables (that is why same size of cable is a requirement), so divide the total current by the number of cables and use this current for voltage drop calculation.

See the previous posting for voltage drop calculation formula: http://cr4.globalspec.com/thread/51446

See also the recent discussion about voltage drop, http://cr4.globalspec.com/thread/52788

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#4

Re: Generator supply volt drop problem

04/15/2010 2:12 PM

supplying a load?

What load?

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Anonymous Poster
#5

Re: Generator Supply Volt Drop Problem

04/15/2010 10:58 PM

Why not shift the generator closer, after all they aren't that big and most are very well silenced. Re-fueling and servicing may be an issue but not one that can't be overcome.

Register to Reply
Member

Join Date: Apr 2010
Posts: 9
#6

Re: Generator Supply Volt Drop Problem

04/16/2010 1:54 AM

Max permissible volt drop is dependant of standard that shall be full fill, as per which standard You shall make installation?

As per latest BS or IEE max volt drop deviation is from source to last point is +/-10% , but in moust countries and local distributions is adopted -6% as maximum.

Practise is that up to your Main distribution board Distribution network can have 2% drop, and you have limit of 4% from Your MDB onwards.

So in case of generator supply You shall consider that for 630KVA up to your MDB it can be max 2%.

If you can tune generator and run it on +2% Un than you can compensate drop and reduce cables.

Summary:

In case of Un=415V on 630KVA load with power factor 0.85 and on 150m run You will have:

2.61% (10.83V) drop with 3x4C240mm cable with current carry capacity 1146A (3x240 per phase)

1.96% (8.12V) drop with 4x4C240mm cable with current carry capacity 1528A (4x240 per phase)

So wee what You can do with gen set regulation, you can save one run.

__________________
lazzarus
Register to Reply
Member

Join Date: Apr 2010
Posts: 9
#7

Re: Generator Supply Volt Drop Problem

04/16/2010 2:06 AM

If You are on 480V level with PF 0.85 You will have:

Lad current 891A Volt drop 9.36V or 1.95% on 3x4C240 cables

Volt drop 14.04V or 2.93% on 2x4C240 cables

See if You can run gen set on +2.5Un % level and go with double runs only

__________________
lazzarus
Register to Reply
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#8

Re: Generator Supply Volt Drop Problem

04/16/2010 3:50 AM

The obvious solution is to use bus ducts. This is generally more expensive initially but is a lot more reliable with lesser volt drop. Otherwise if the loads are inductive then capacitors are also applicable.

__________________
Better not count the cent if the risk is many many dollars.
Register to Reply
Member

Join Date: Apr 2010
Posts: 5
#9
In reply to #8

Re: Generator Supply Volt Drop Problem

04/16/2010 5:03 AM

Hi Folks,

sorry, some more info to get the big picture. LV Voltage is 400v +/- 10% and the generator volt-drop is 1 - 1.5% as the rest of the 4% permissable volt-drop is from the LV Panel to the final sub circuits. The designed load is 504KW. It is an external installation and as stated the genset is approx 150m from LV Panel and cannot be located nearer - unfortunately!

My simple thinking is - can the generator produce a higher voltage that compensates the volt-drop arriving at the LV Panel within the stated 400v +/- 10% ? Or can a Voltage Compensation Panel be installed at the midpoint of the genset cabling to boost the supply voltage ? or is there some other alternative to avoid 12 no. cables per phase ?

thanks

GC05

Register to Reply
Member

Join Date: Apr 2010
Posts: 9
#10

Re: Generator Supply Volt Drop Problem

04/16/2010 5:59 AM

Your load is 504KW or 504KVA? it is calculated load or diversified

Supply line shall be calculated for diversified load, usually Kd factor is 0.7

If it is 504KVA your current will be 856A for standard non compesat power factor 0.85, and drop will be 8.99V or 2.17% for 3x240 per phase.

If You calculate for diversified load your sizing shall be for 353KVA or 598A with 6.28V drop or 1.51%

You need 3x3C240 cables or 9x240 single core cables (3x240 per phase)

From where you get 12x240 per phase?

__________________
lazzarus
Register to Reply
Anonymous Poster
#11

Re: Generator Supply Volt Drop Problem

04/16/2010 7:48 AM

If I am running power long distance I always think of transformers you can do it the same way the utility company does it. Lets say your gen voltage is 120/208v you can set a transformer at the genset and boost it up to 480v and then re-transform it down at the load. Or if your genset voltage is the same as your load side power you (say its a 480V load) then install a 480V - 480V transformer at the load side and use the available taps built into the transformer to achieve the proper voltage. Or use a buck/boost autotransformer system to adjust for your voltage drop.

Remember, you will be able to eliminate your voltage drop, but you will transform it into a power drop. So make sure the generator is rated high enough to compensate the load.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#12

Re: Generator Supply Volt Drop Problem

04/16/2010 11:36 AM

Quote GC05 "LV Voltage is 400v +/- 10% and the generator volt-drop is 1 - 1.5% as the rest of the 4% permissible volt-drop is from the LV Panel to the final sub circuits. The designed load is 504KW. or is there some other alternative to avoid 12 no. cables per phase ?"

You do not need 12 cables per phase. You need to check you calculations. Have you read all of the posts or just ignored them.

Gc05 response is requested.

Register to Reply Score 1 for Good Answer
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#13
In reply to #12

Re: Generator Supply Volt Drop Problem

04/16/2010 12:41 PM

"or is there some other alternative to avoid 12 no. cables per phase ?"

permit me repeat lv busduct. pl check the ROI with attendant benefits.it may work out due to its simplicity and reliability.

__________________
Better not count the cent if the risk is many many dollars.
Register to Reply
Member

Join Date: Apr 2010
Posts: 5
#18
In reply to #12

Re: Generator Supply Volt Drop Problem

04/19/2010 3:44 AM

Apologies, see my latest post

GC

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#19
In reply to #18

Re: Generator Supply Volt Drop Problem

04/19/2010 11:26 AM

Here is a voltage drop calculator. Do it yourself.

http://www.fyxm.net/british-standard-voltage-drop-75464.html

Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#14

Re: Generator Supply Volt Drop Problem

04/16/2010 1:35 PM

Greetings GC05,

Besides the viable solutions posted, have you considered a buck/boost transformer set at the end of the run prior to the load?

http://www.powertransformer.us/buckboosttransformers.htm

I don't know if these are compatable with the voltage you are using but I thought I would give it a shot.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#15

Re: Generator Supply Volt Drop Problem

04/17/2010 3:24 PM

GC05 & Friends,

Another approach is to have the generator's voltage regulator be sensing the voltage at the distribution panel 150m away from the generator. I see no design difficulty in doing this and it would allow the generator to automatically correct the voltage as the load changes. This may require a consultation with the generator's manufacturer to ensure that it is done correctly.

--JMM

Register to Reply
Anonymous Poster
#16

Re: Generator Supply Volt Drop Problem

04/17/2010 6:06 PM

As WAREAGLE said, "Check your calculations"!

12 cables of 240 square mm is ridiculous for the least and therefore you are missing thepoint somewhere in your calculations. There are tables for voltdrop on cables available from cable manufacturers if you want it easier...

Register to Reply
Member

Join Date: Apr 2010
Posts: 5
#17
In reply to #16

Re: Generator Supply Volt Drop Problem

04/19/2010 1:45 AM

Dear Wareagle & others,

apologies, I have been trying to get hold of the cable calcs from our Turkish Designers to verify. They have been promised today. So far their info has been by word of mouth and taken on trust. As soon as I receive I will review & maybe post for clarification.

I appreciate the various recommendations thus far.

thanks

GC

Register to Reply
Member

Join Date: Apr 2010
Posts: 5
#20

Re: Generator Supply Volt Drop Problem

05/04/2010 1:40 AM

Hi Folks,

Apologies for the silence but a few serious things have been happening here. Needless to say I have not received the Electrical Designer's cable sizing calculations. But worse than that, the Project has been cancelled ! Looks like we're all out of a job and total staff affected is around 400 personnel.

Thanks again for the advice unfortunately could not implement it!

GC

Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); GC05 (4); Jans (2); jmueller (1); KJK/USA (1); lazzarus (3); msamad (1); peterg7lyq (1); RDGRNR (1); wareagle (3)

Previous in Forum: Making Micro Control Based Helicopters   Next in Forum: there is no response while relay testing on dry contact with ISA

Advertisement