Fan Performance

04/18/2010 11:14 PM

what is expected drop in performance in fan tip clearance excees 30mm in one side of fan ring?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: fan performance

04/18/2010 11:22 PM

What's the ring for? Is this a ducted fan?

Reply
2
Power-User

Join Date: Nov 2009
Posts: 296
Good Answers: 27
#2

Re: fan performance

04/19/2010 2:44 AM

100% if the fan is 60 mm diameter.

__________________
I have no special talent. I am only passionately curious. Albert E
Reply Good Answer (Score 2)
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#3

Re: fan performance

04/19/2010 3:23 AM

No difference in free running airflow but its will not produce specified static pressure under the loaded (fully or partially inlet/outlet blocked) conditions.

Reply Score 1 for Good Answer
Reply to Forum Thread 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Kaisan (1); lyn (1); rakesh_semwal (1)

Previous in Forum: Prensa Hidraulica de 100 Toneladas   Next in Forum: Wet Compression

Advertisement