what is a difference between low forward power and reverse power in generator?

04/21/2010 11:04 AM

is it necessary to trip generator during reverse power?

Also posted in: also posted in Electrical Engineering
Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Mar 2010
Posts: 33
Good Answers: 2
#1

Re: what is a difference between low forward power and reverse power in generator?

04/21/2010 11:26 AM

Here is some background on reverse power...forward power should be the opposite

Reverse kVAR- Reverse kVAR can happen when the gen set has lost excitation and the system returns vars to the gen. If the load has a leading power factor the gen set will also see a reverse power factor.

Reverse power - watts and vars well reverse power combined with power factor. watts don't eqaul vars

When will it happen? - Leading Power Factor can be a cause. Very low loaded UPS with power factor correction that serves pdu's with power factor correction built into, combined with all the induction motors having vfd's will have a leading power factor. the common one is loss of excitation

how will it affect the alternator? - it will induce currents in the rotor at 120hz or 100hz if your in Europe. also the impedance of the rotor sturcture is so high that when you have you I^2R the heat build up can start to weld.

What should be done during reverse...? - When that happens the gen set should be disconnected from the system.

__________________
guest
Reply
Participant

Join Date: Apr 2009
Posts: 1
#2
In reply to #1

Re: what is a difference between low forward power and reverse power in generator?

04/21/2010 11:24 PM

thanks.

Reply
Anonymous Poster
#3
In reply to #1

Re: what is a difference between low forward power and reverse power in generator?

04/22/2010 12:13 AM

Can we trip steam turbine also? At present we are not tripping turbine during reverse power only gen.breaker is tripping.

Reply