Re: what is a difference between low forward power and reverse power in generator?
04/21/2010 11:26 AM
Here is some background on reverse power...forward power should be the opposite
Reverse kVAR- Reverse kVAR can happen when the gen set has lost excitation and the system returns vars to the gen. If the load has a leading power factor the gen set will also see a reverse power factor.
Reverse power - watts and vars well reverse power combined with power factor. watts don't eqaul vars
When will it happen? - Leading Power Factor can be a cause. Very low loaded UPS with power factor correction that serves pdu's with power factor correction built into, combined with all the induction motors having vfd's will have a leading power factor. the common one is loss of excitation
how will it affect the alternator? - it will induce currents in the rotor at 120hz or 100hz if your in Europe. also the impedance of the rotor sturcture is so high that when you have you I^2R the heat build up can start to weld.
What should be done during reverse...? - When that happens the gen set should be disconnected from the system.