04/22/2010 3:18 AM
210mw steam turbine recently gone for overhauling. After completion when load raised to 160mw at the time boiler got tripped on loss of flame. during this time turbine thrust pad (hp turbine side) temperature went up to 160 deg.c. on inspection thrust pad got wore.but the axial shift values are within limit. actually it was -.14mm. (Trip value is + OR - .8mm) thrust bearing temperature is normal. Float of our turbine is .18mm. what may be the reason?
Re: thrust pad temperature rise
04/22/2010 3:28 AM
Thrust pad temperature rise is most likely (almost entirely) due to loss of lubrication
This may happen due to-
a) Lubrication failure
b) Excessive axial loading (film squeezed out)
It is assuming it was behaving well till 160MW, you must be of course raising the load slowly and most likely there was no signal on the operations - temperature of thrust pad/vibration/...
How is the physical appearance of the pads? (except wear out - discoloration/pitting etc?)
04/22/2010 3:51 AM
about .1mm of metal removal in all pads
04/22/2010 10:08 AM
When I said visual - what was the surface of the thrust pad looking like - and what was the collar like?
The material removal is uniform? ie are there any serrations- pittings,... or the face is still as polished ?
Is there a possibility of unbalanced thrust due to the type of trip?
The thrust bearing is new or the old one? Are you sure the wearout has taken place due to this trip ? it might as well be due to natural causes?
04/22/2010 6:32 AM
Most likely overload.
What did the turbine speed do during the boiler trip? What did the pump suction pressure and temperature do?
04/22/2010 6:49 AM
turbine speed 2950 rpm .auxilary lub oil pump starts.oil pressure 2.14 bar ,53 deg .c
Re: Thrust Pad Temperature Rise
04/23/2010 1:25 AM
So you were running on turbine driven lube oil pump, and when boiler tripped it switched over to electric motor driven lube oil pump?
If so, then that is your problem!! Your lube consol is not operating properly and you had a momentary lack of lube oil during the switch over.
A very common problem. You need to optimize the controls on your lube oil consol and check out the pump switching.
Good Answers: 27
04/23/2010 3:03 AM
Got to go along with Steve. You may also want to fit a bladder vessel if not already there, and if there is one then check that it is correctly charged. This helps to smooth the pressure dip when changing over pumps.
I have no special talent. I am only passionately curious. Albert E
04/25/2010 12:32 AM
Normally the thrust pad git wore thats may due of number of time of run and stop the machine and you have to avoide to do this phenomena because time of start up and shudown lead the rotor to possess back and forth movement till arest to its running position.
Also you have to check the oil vescosity and monthly doing analysis and git the result.
you have to check the lube oil pump strainer if there any forigen materials accumelated and cause decrease to the oil supply as well as to check the oil filters.
Your machine actually should have voting system to allow the machine trip befor gitting to high tempreture.
you have to do vibration analysis to know the real problem if its umbalance or preloaded or misalingment and etc...
All the best
04/26/2010 2:26 AM
thank you vcm inspector. now we are doing all the recommendations given by you. some other areas also we are going to concentrate. after completion of these things ,if same thing occurs ,i will contact you.
04/28/2010 4:27 AM
Ummm, did you read my post, because I really am pretty sure you have a problem with the pump switch over..
05/05/2010 12:49 PM
Unit was running to 160 MW it means that all parameters during rolling and loading of the set was normal, after AOH very extensive attention required as during coasting down period set passes through the critical speed, during this period vibrations of T.G. set rise, and bearings settle at position. In this case it is suspected that T.G. set remains in critical zone for long time that result in thrust bearing failure, however by opening vacuum breaker i.e reducing condenser vacuum , coasting down period can be reduced and there is possibility to reduce the damage to the thrust bearing.
05/06/2010 5:18 PM
Sitting a long time in the critical absolutly does not have anything to do with thrust bearing damage.