Surge Arrestor

04/22/2010 4:13 AM

I want to know what are the factor that defines the rating of surge arrestor.

Why the rating of a class 3 surge arrester is 198kV while it is connected bewteen phase to ground for 220kV switchyard.

Again what the current rating 10kA indicates to.

__________________
partha sarathi pattanaik
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Member

Join Date: Mar 2010
Posts: 7
#1

Re: surge arrestor

04/22/2010 5:08 AM

I m not sure, but as you are saying the switch yard voltage is 220 KV. This is the line voltage and not phase voltage. We are connecting the surge arrestor in between phase and the ground.

Now, in your case, the phase to ground voltage is 220 KV/1.73 which is around 128 KV. So, you will require a surge arrestor which capacity should be more than 128 KV.

The function of surge arrestor is to arrest the high voltage surges on the line (this surges may be because of grid fluctuations or lightening) and to protect the connected equipments from high voltage. So, surge arrestor provide low resistance path to high voltage and allow current to pass through it, actuating the protection relay to trip the feeder.

The current 10 KA indicates the amount of current it can carry safely.