Power factor for Induction Generator

04/22/2010 5:38 AM

In wind turbines, induction generator is used to produce electricity from wind. These generator is directly connected to grid supply.

Can anybody tell whether the power factor for induction generator is lagging or leading? If it is leading, why wind turbine manufacturers uses capacitor panels to compensate power factor?

Register to Reply
Pathfinder Tags: Wind turbine generator
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Nov 2009
Location: PA
Posts: 83
Good Answers: 1
#1

Re: Power factor for induction generator

04/22/2010 10:15 AM

The power factor for induction generator is lagging as it need vars for magnetising the stator so they need capacitors to compensate.

Are you working in wind farm?

Register to Reply
Member

Join Date: Mar 2010
Posts: 7
#2
In reply to #1

Re: Power factor for induction generator

04/23/2010 12:02 AM

Yes, i am.

But the point is induction generator supplies active power to grid and consumes reactive power from grid. In which quadrant, the resultant current vector is?

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4
In reply to #1

Re: Power factor for induction generator

04/23/2010 9:06 AM

2nd quadrant since power is generated to the grid.

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#3

Re: Power factor for Induction Generator

04/23/2010 5:08 AM

Induction generator operation would mean that it is drawing its excitation power from the grid. This is taken in the form of stator drawing current which should have magnetizing armature reaction. (Armature reaction is demagnetizing when stator current is of lagging power factor, cross magnetizing at unity power factor and magnetizing at leading power factor). So for the purpose of analysis, stator would carry two currents. First the load current, power factor of which is decided by the nature of load and second magnetizing current which would be of zero leading power factor. Net power factor will be decided by vectorial sum of the two currents.

Register to Reply
Anonymous Poster
#5

Re: Power factor for Induction Generator

04/23/2010 10:33 AM

Just google -

Self Excited Induction generator

Capacitor Excited Induction generator

or

Induction generator Excitation

and you will find a lot of good papers and articles (and quite a few are for the Wind Energy)

A few are from the theoritical aspect also from different universities and also the theory of AC circuits link

Register to Reply
Associate

Join Date: Sep 2009
Posts: 26
#6

Re: Power factor for Induction Generator

04/23/2010 11:41 AM

If a generator is a permanent magnet, then the power factor is lagging. However, if it is a synchronous generator, the level of excitation would determine whether power factor is leading or lagging. If it is over-excited, then power factor would be leading, and if under-excited, then power factor would be lagging. Generally, power factors of large machines are adjustable. Possibly, part of the reason wind turbine manufacturers use large capacitor banks is to cancel out the reactive L.