We have HT induction motor with specifications - 6500kW, 11kV, 348A, 1485rpm, 0.917 full load pf, starting current - 1620A. This motor drives a centrifugal air compressor.
To start this motor, we synchronize our CPP with the grid and disconnect the CPP from the grid after the motor has started. There are 8 DG sets in CPP of which 6 are started and synchronized for motor starting. The DG set specifications are - 11kV, 8145kVA, 428A, 750rpm, Xd - 1.5 pu, Xq - 0.78, X'd - 0.26, X'q - 0.78 on generator MVA base. CPP base load at the time of motor starting is about 6.0MW.
CPP is synchronized with the grid through 110/11kV, 40MVA, 12% pu impedance transformer. The nearest grid substation is located 4.5kM away from the plant.
What are the factors which influence the division of starting MVA of this HT motor among CPP DG sets and the grid.