HT Motor Starting

04/27/2010 10:06 PM

We have HT induction motor with specifications - 6500kW, 11kV, 348A, 1485rpm, 0.917 full load pf, starting current - 1620A. This motor drives a centrifugal air compressor.

To start this motor, we synchronize our CPP with the grid and disconnect the CPP from the grid after the motor has started. There are 8 DG sets in CPP of which 6 are started and synchronized for motor starting. The DG set specifications are - 11kV, 8145kVA, 428A, 750rpm, Xd - 1.5 pu, Xq - 0.78, X'd - 0.26, X'q - 0.78 on generator MVA base. CPP base load at the time of motor starting is about 6.0MW.

CPP is synchronized with the grid through 110/11kV, 40MVA, 12% pu impedance transformer. The nearest grid substation is located 4.5kM away from the plant.

What are the factors which influence the division of starting MVA of this HT motor among CPP DG sets and the grid.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: HT Motor Starting

04/28/2010 10:57 PM

You have a problem of starting large motor? This is typical to large reactive demand from the grid.by Inductive load We resolve this kind of disturbance, when using the right and specific Equalizer operate in real time ,with Harmonic filters .We are specialist on electric disturbance resolve as Power quality expert. We could help if you want. Saada Joshua Gabriel V.P. Engineering Alternative Power System's saadaj@netvision.net.il Alternativepowersystems@gmail.com Tel: 972(0) 88652424- 972(0) 774100494 Cell: 972(0) 546566191 Tel/fax on demand: 972(0) 88652424 Electrical Test Engineer: License Nr: 085195 Senior Electrical license Nr: 007922

Register to Reply Off Topic (Score 7)
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#2

Re: HT Motor Starting

04/29/2010 2:48 AM

This is indeed a tricky one and i'm sure should best br answered by High voltage experts or practitioners. However you may find useful info here

http://www.lmpforum.com/inforum/Advantages-Ht-Motors6-t2512.html

Best of luck

__________________
Always learning
Register to Reply
Commentator

Join Date: Nov 2006
Location: Dubai
Posts: 67
Good Answers: 1
#3

Re: HT Motor Starting

04/29/2010 6:38 AM

I guess impedance of the two sources would determine how starting load is divided between the two....but am not sure. I could be way wrong on this.

Register to Reply
Anonymous Poster
#4

Re: HT Motor Starting

04/29/2010 7:01 AM

Just Confirm each generator is around 1500KW in rating. Presently they are Solid State Starters, Soft Starters which are designed for 15KV, 22000 HP which reduces a lot of your starting hi-cups as stated. Its becomes more complicated to set a system on a continuous basis to be started in the above manner.

Register to Reply
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#5

Re: HT Motor Starting

04/29/2010 9:31 AM

There is absolutely no problem in starting this HT motor with the set up as explained in the question. I want to what are the factors that decide the division of the starting MVA of the HT motor between CPP and the grid.

Register to Reply
Anonymous Poster
#6
In reply to #5

Re: HT Motor Starting

04/29/2010 1:06 PM

The missing ingredient is the Utility short circuit capacity at the 40MVA transformer primary. The 12%Z seems high for the transformer alone. With a robust utility, it may go without the generators. I am assuming the motor is line started. The centrifugal fan does not have a starting torque problem, but the high inertia of the fan will stretch the acceleration time and stress the motor rotor bars. stretch the time between starts. Try to limit the drop in voltage to 10% of motor voltage. I think the division of load will depend on the speed of the generator regulators, and would change the division during acceleration. Off the top of my head. Tony

Register to Reply Score 1 for Good Answer
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#7
In reply to #6

Re: HT Motor Starting

05/02/2010 3:18 PM

This is a general practice.The sharing depends on trfo tap settings grid fault level and governor and avr settings.The trafo may support typically 60% starting mva.

__________________
Better not count the cent if the risk is many many dollars.
Register to Reply
Register to Reply 7 comments