How to Calculate 3 Phase Transformer For 1 Phase Load?

04/28/2010 10:06 AM

E.g We have 1000 Kw.1 phase load for that I want to select three phase distribution transformer.Can I select the 1000 Kw Transformer or what is the calculation?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#1

Re: How to Calculate 3 Phase Transformer For 1 Phase Load?

04/28/2010 10:55 AM

Transformers are rated for KVA, assuming unity power factor You need 3x1000KVA transformer, and also you will have to make a plan to load other two phases.Otherwise you ll end up with huge unbalanced current.

Register to Reply
4
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: How to Calculate 3 Phase Transformer For 1 Phase Load?

04/28/2010 12:06 PM

If the single phase 1,000 kW load is a single load, then what Rakesh mentioned is correct.

But if the 1,000 kW load comprises of several individual single phase loads, then distribute the loads to 3 different groups, as equally as possible. Then multiply the largest group load by 3 and the result (converted to kVA using average power factor) should be the transformer capacity.

For example, if the individual loads are:

Load 1 – 100 kW

Load 2 – 150 kW

Load 3 – 200 kW

Load 4 – 250 kW

Load 5 – 300 kW

Load groupings:

Group 1: Load 1 + Load 4 = 350 kW

Group 2: Load 2 + Load 3 = 350 kW

Group 3: Load 5 = 300 kW

The maximum group load is 350 kW

The 3 phase transformer capacity requires to supply 350 x 3 = 1,050 kW

Assuming average power factor of the loads is 0.8, the transformer capacity is 1,050/0.8 = 1,312 kVA. Considering some reserve loads, you can select a 3 phase transformer of size 1,500 KVA or more.

Each group of loads shall be connected to each phase of the transformer.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 4)
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#3
In reply to #2

Re: How to Calculate 3 Phase Transformer For 1 Phase Load?

04/28/2010 12:28 PM

I think your assumption is right as it is very unlike to have a single load of 1000KW.

GA.

Register to Reply
Anonymous Poster
#4

Re: How to Calculate 3 Phase Transformer For 1 Phase Load?

04/29/2010 1:41 AM

Why don't you choose single phase transformer? The cost would be lower than a 3 phase. Or you also need 3 phase system?

regards

nikolay

Register to Reply
Associate

Join Date: Feb 2010
Posts: 40
#5

Re: How to Calculate 3 Phase Transformer For 1 Phase Load?

04/29/2010 3:14 AM

Mr. MS is right and when design a transformer capacity consider 30% more than counsumer load.

Register to Reply
Register to Reply 5 comments