Motor Replacement & Torque Problem

05/04/2010 12:30 PM

We have Cement transport Fan(s) driven by a motor (Say Motor-A) of 4 KW (ABB).We want to replace it with another motor (Say Motor-B) of 4 KW of other brand (Siemens) due to its availability and cost.

Motor A (ABB 4 KW) is Delta Connected at 400 V and Motor-B (Siemens 4 KW) should be connected in Star configuration at 400 V. (Available Voltage is 400 V)

Can Motor-B will provide enough torque to Drive the Fan in Star Configuration?

Name Plate of Both motors are

Motor-A :( ABB 82.246 %)

4 KW. 2850 RPM, 50 Hz, 400/690 V (Delta/Star),7.8/4.5 A, PF 0.90

Motor-B :(Siemens ( Efficiency 83.9 %)

4 KW. 2905 RPM, 50 Hz, 400 V (Star), 8 A, PF 0.86

Motor A is running at 2.97 KW (Current is 5.8 A i-e 74.3 %) under normal condition.

Torque at 2850 RPM and 2.97 Kw will be T = 2970/(2850*(6.28/60))= 9.951 N.m

When Motor-B (Siemens) will be connected its speed will be 2905 RPM

Required torque at 2905 RPM will be T= 10.3392 N.m (using affinity Laws) and Power required to produce this torque will be 3.145 KW

Is Motor-B is capable to produce this torque in Star Configuration?

What will be the Power for this torque?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Motor Replacement & Torque Problem

05/04/2010 1:29 PM

The power rating of the motor (kW in your case) is a short-hand way of expressing torque at a given speed. So if the speed of each 4kW motor is the same, the torque is the same. How the motors are wound internally has nothing to do with it.

Now in the case of these two specific motors, there is a very slight difference in speed and as you have correctly observed, the Siemens motor is a little faster, so technically, it is producing ever so much less torque than the ABB motor. Assuming he 4kW rating is essentially accurate in both, then the Siemens motor is a potential problem. But it appears you have correctly ascertained the required power at the shaft and it is less than what the Siemens motor will be able to deliver, so no problem.

Don't get caught up in the Star or Delta connection issue, it is a red herring here. That has only to do with how the motor was made, not with how it will perform at the rated voltage.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Motor Replacement & Torque Problem

05/04/2010 3:56 PM

I totally agree to what JRaef said.

Here is just added few words for more clarification:

I understood, the main concern here is the Delta/Star configuration of motor A.

What actually "4 KW, 2850 RPM, 400/690 V (Delta/Star), 7.8/4.5 A" mean for motor A:

(1) If you connect the motor stator windings in Delta configuration and apply 400V to the terminals, the motor will produce maximum 4 KW power with full load current 7.8 A and its full load torque at 2850 RPM.

(2) If you connect the motor stator windings in Star configuration and apply 690V to the terminals, the motor will produce maximum 4 KW power with full load current 4.5 A and its full load torque at 2850 RPM.

(3) If you connect the motor stator windings in Star configuration and apply 400V to the terminals, the motor will produce maximum 4/3 = 1.33 KW power with full load current 4.5 A, the full load RPM will be slight less than 2850 RMP and its full load torque will be close to 1/3rd of the rated torque.

In terms of motor output, both condition 1 and 2 are same but the motor is flexible to use for both 400V and 690V.

Because of the Delta/Star winding options, the motor A also can be used for Start/Delta starting and if it is started with Start/Delta starting, the condition 3 is applied first, then it moved to condition 1 after few second.

The motor B has only Start connection with 400V rating. So, if 400 V is supplied to its terminal, it will produce maximum 4 KW power and its full load torque at 2905 RPM. The full load current is 8 A.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)