Thyristor Controlled Motor

05/05/2010 7:53 AM

In direct arc furnace we have 3 dc motors(6 HP each) controlled by thyristors. One motor lost its torque in between and stopped with a humming. We thought its motor winding problem and replaced. But new motor also had same problem. Supply is showing less voltage and more current than normal. What is the problem with the thyristor panel?

Register to Reply
Pathfinder Tags: DC motor Thyristor Voltage
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Thyristor Controlled Motor

05/05/2010 9:22 AM

Hi HIT;

You've got a few things to check: with the power down, measure drive-to-motor wiring insulation respect to ground, if its OK proceed to disconect your motor and measure the resistance from Driver terminals A+ and A- to AC input lines, compare to another motor driver that is known good, if you find a too low resistance, you most likely have a bad thyristor and/or diode.

Yahlasit

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#2

Re: Thyristor Controlled Motor

05/06/2010 12:00 AM

First thing: Cheque for field amps and volts.

If they are not within spec then you may have a shorted or open field.

Without field flux you do not develop torque.

T=k*Φ*Ia

Vt= Ra*Ia + k'*Φ*ω

Ra*Ia is usually less than 10% of Vt.

Φ varies with If, and is approximately linear at low strength, tends to saturate at rated If.

Essence of above is that if Φ is low T drops and so does the terminal volts for a given rpm.

Since the drive is probably speed regulated it applies more current up to current limit. But without field it does not develop torque to overcome the losses.

Register to Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#3
In reply to #2

Re: Thyristor Controlled Motor

05/06/2010 4:53 AM

Thanks for your trouble shooting technique.The real problem was with a covered pulley. The metallic rope jumped out and mechanical load increased.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#4
In reply to #3

Re: Thyristor Controlled Motor

05/06/2010 11:44 PM

Why do operations always call the E/I department first?

Register to Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#5
In reply to #4

Re: Thyristor Controlled Motor

05/07/2010 1:38 AM

In this plant after electrical checking,mechanical department solve the problem,but maximum are electrical faults.your method will be useful for further faults.thank you very much.