Neutral tripping characteristic when circulating current happen(genset parallel)

05/08/2010 2:12 AM

Hi All,

When one of neutral switch not open when genset in parallel, it will produce circulating current...

1. What is circulating current

2. What is neutral tripping characteristic

thks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#1

Re: Neutral tripping characteristic when circulating current happen(genset parallel)

05/08/2010 11:33 PM

Hi,

When you are synchronising the Gensets the following Parameters are mandatory -

1 Equal Voiltage of the Alternators to be synchronised.

2. Equal Speed of the Engines

3. Same Phase Sequence - Direction of Phase Rotation

4. Same Phase / Load Angle of the Alternators - I Mean to Say the Potential Difference Between the Same Phase of Different Alternators.

If First two Cases are not matched exactly & balance two are ok , then you can synchronise the Genset but the Circulation current will flow between the Alternators because of the uneuqal Voltage & Frequency.

Point to be noted is although after synchronising the Alternators the Terminal Voltage on the Bus Bar is Same the Generated Voltage of the Alternators is same what has been set during the Initial Set Up.

The Amount of this Circulation current Depends upon the Voltage & Frequency Differences.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#2

Re: Neutral tripping characteristic when circulating current happen(genset parallel)

05/09/2010 5:23 PM

Circulating current = current circulating between the two generators and due to differences in the voltages of the same phases.

Since the Generators have been synchronised successfully at the start, the frequency and phase sequences should be correct and OK. The phase to phase voltage between identical phases should be ZERO ideally, but some difference can appear due to settings and/or fluctuations or differences in characteristics...hence a circulating current between the generators. This should be kept very low.

Neutral tripping: Due to the same as per above, and to some imbalnce in the load, there will be some neutral current flowing also. This is also controlled and should remain minimal.

Register to Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#3

Re: Neutral tripping characteristic when circulating current happen(genset parallel)

05/09/2010 10:15 PM

Your statement of the problem is lacking vital information -

1. Have these generators ever been paralleled before ?

2. Have these generators ever run correctly in parallel before ?

3. Was cleaning, maintenance or other repair work performed immediately before this problem started ?

These answers can help prevent "tail chasing" and guessing.

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

CoronaCameraMan (1); LAA_Lucke (1); vishram lele (1)

Previous in Forum: Capacitor value   Next in Forum: Tremendous High Pressure of SF6 Gas
You might be interested in: Neutral Density Filters, Receptacle Testers, UV Filters

Advertisement