CURRENT CARRING CAPACITY

05/08/2010 8:54 AM

Current carrying capacity for 40x10 sq.mm Aluminium Bus bars

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Mar 2010
Posts: 105
#1

Re: CURRENT CARRING CAPACITY

05/19/2010 4:13 AM

Dear Sir,

A current density 1 amp per sq.mm is taken as a basic design factor.

Taking into factors like heating , location, stacking , outside temprature the

normal practice is to employ a factor of 0.7. So you can safely load upto 300

Amps and with a overload of 10 to 15 % for about 10 minutes.

Manroop. Chennai-33