Hi I'm still confusing because I'd like to calculate the saving money:in fact,my company has a 50KVA power supply,a power factor of 0.86 and after one year,my company needs to use 80KVA.my question is how much should I save if I want to improve my new power factor to 0.86.(NB:the cost per 1KVA is 30$).
kind regards
Impossible n'est pas Camerounais
Pathfinder Tags: Power Factor power supply
Re: Power Factor Correction
02/15/2007 12:11 AM
I have also same question to ask. Kindly reply if any answer
Thank you
Kemsindia@gmail.com
02/15/2007 2:10 AM
Dear Sir,
We have high speed real time automatic power factor correction system
if your are interested pl. send your requirement on automac.paras@gmail.com
Paras Patel
02/15/2007 2:07 AM
dear sir,
we have high speed real time automatic power factor correction system,
this system is very smooth & transient free
if you are interested pl. contact in india on 09377542899 or mail your requirement on automac.paras@gmail .com
Paras Patel
02/15/2007 2:29 AM
POWER FACTOR IMPROVEMENT 80kVA
The present average power factor = 0.86
The present Recorded Maximum Demand = 80KVA
Therefore the average max. load = 80x0.86 =69KW
Recommended PF = 1.00
RMD at improved PF = 69/1.00 =69KVA
Reduction in KVA = 80-69 =11.2KVA
Annual Saving due to reduction in RMD = 11x$30 x 12 =$3,000
Additional KVAr requirement = KW x (Tan f1-Tan f2)
= 69(0.593-0.000)
= 41KVAr
POWER FACTOR IMPROVEMENT 50kVA
The present Recorded Maximum Demand = 50KVA
Therefore the average max. load = 50x0.86 = 43KW
RMD at improved PF = 43/1.00 = 43KVA
Reduction in KVA = 50-43 = 7.0KVA
Annual Saving due to reduction in RMD = 7x$30 x 12 = $2,000
= 43x(0.593-0.000)
= 26KVAr
02/15/2007 6:37 AM
Happy!! thank you verry much
02/15/2007 7:13 AM
Where do you come up with the angles f1 and f2.
I know they are the angle of the power factor but how does that relate to the power factor of .86?
02/15/2007 7:17 AM
I assume a power factor of 1.00 has an angle of zero?
a Power facotor of .50 would be ????
02/28/2007 8:20 AM
Use your calculator or look up tables to find the Cosine of 0.5!