Starting current and torque in star cicuit

05/11/2010 7:07 AM

Dear Fellows,

I want to make it clear that;

If we start the motor direct on line (Delta) then its starting current will be 6-8 times > then full load current and torque will be 100-200% then the full load torque. But if we start the motor in Star circuit, then what would be its starting current and torque? Can any body explain with detail or with formulas?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: Starting current and torque in star cicuit

05/11/2010 8:19 AM

Look here.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#2

Re: Starting current and torque in star cicuit

05/11/2010 8:47 AM

When the windings of a 3-phase motor are connected in STAR:

  • the voltage applied to each winding is reduced to only (1 /.'/'3) [1 divided by root three] of the voltage applied to the winding when it is connected directly across two incoming power service line phases in DELTA.
  • the current per winding is reduced to only (1 /.'/'3) [1 divided by root three] of the normal running current taken when it is connected in DELTA.

  • so, because of the Power Law V [in volts] x I [in amps] = P [in watts],

    the total output power when the motor is connected in STAR is:

    PS = [VL x (1/.'/'3)] x [ID x (1/.'/'3 )] = PD x (1/3) [one third of the power in DELTA]

    where:
    VL is the line-to-line voltage of the incoming 3-phase power service
    ID is the line current drawn in DELTA
    PS is the total power the motor can produce when running in STAR
    PD is the total power it can produce when running in DELTA.

  • when the motor is connected in STAR is that the total output torque is only 1/3 of the total torque it can produce when running in DELTA.
Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Starting current and torque in star cicuit

05/11/2010 12:08 PM

It is already explained.

Here is some additional:

Starting current: If the motor is started with star winding, the voltage applied to the winding is 1/√3 of the supply voltage and hence, the current is also 1/√3 of the Delta winding starting current.

Starting Torque: Torque developed is directly proportional to square of voltage and so the star winding starting torque is (1/√3)2 = 1/3 of the Delta winding starting torque.

Please see the thread http://cr4.globalspec.com/thread/54100 for avoiding the confusion about star/delta configuration of motor.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Anonymous Poster
#4
In reply to #3

Re: Starting current and torque in star cicuit

05/12/2010 6:07 AM

Thanks to all.

It means that we can not run such a motor in star where a high starting torque require such as conveyor belts air compressors as in star config, the torque reduces 1/3 of motor full load torque. Am I right?

2nd question, what is the max starting torque can produce an AC motor?

Best Regards

Reply
Anonymous Poster
#5
In reply to #4

Re: Starting current and torque in star circuit

05/12/2010 8:15 AM

Compressor load demand also is low when the RPM is low. That hence may not be a problem.

What usually is done is that you get the load characteristics curve - speed/torque characteristics (or speed- power and convert into the speed torque)

get the same for motor. Then overlap one above other, the intersection will give you the operating point.

If you see the load torque is more than the motor, it will not start.

Conveyor is another problem, since if it is fully loaded, the torque in the start is highest (static friction) then it goes down. So either

Take the motor of higher capacity.

Start the conveyor without load and then start loading it.

Slip Ring Induction motors ( will have better starting torque) also more loss. There are certain double cage motors acting with high resistance cage at start (almost like SRIM) and then as the RPM increases it works as normal SQIM.

DC Motors - best starting torque.

Variable Frequency Drives - that may provide you with high starting torque (even there are VFDs that can give > FL Torque at start)

All this decision will be based on your load characteristic curve. Y must take care of the starting torque, in conveyor and similar the requirement is taken to be 20% higher - and although VFD will deliver it, whether motor shaft can withstand it or not is questionable.

BTW: Smaller Pumps, compressors etc at our place are usually started with star-delta without any problem.

Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Alanvaderi (1); Anonymous Poster (2); msamad (1); RDGRNR (1)

Previous in Forum: cable trench   Next in Forum: Remote Control Help

Advertisement