Eyewash Station - Water Hammering

05/12/2010 2:39 PM

Greetings all. I'm baffled and in need of some help. I have an eyewash station that is attached to a wash basin. The eyewash is feed thru two stainers (one hot, one cold) and then into a mixing valve to set the temperature, all below the basin. The pipe comes up and is split; one pipe feeds the eyewash and the other to valve with a hose. My problem is when I turn on the eyewash I get water hammering and water rapidly pulsing thru the eyewash and it becomes unusable. I cleaned strainers and blew air thru all lines to remove any possible obstructions, with no change. I can't figure out the problem. Thanks for your answers.

__________________
I refuse to succumb to the will of an inanimate object!
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#1

Re: Eyewash Station - Water Hammering

05/12/2010 3:56 PM

Does the problem persist if you close one valve (hot/cold) at a time and then run the eyewash?

Sort of sounds like a mixing valve issue. Too much pressure? Too little?

__________________
Semper Ubi Sub Ubi
Register to Reply
Active Contributor

Join Date: Mar 2010
Location: New York, the lakeside
Posts: 20
#2
In reply to #1

Re: Eyewash Station - Water Hammering

05/12/2010 4:23 PM

Yes. The problem exists running hot or cold, and increasing and decreasing water pressure.

__________________
I refuse to succumb to the will of an inanimate object!
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#3
In reply to #2

Re: Eyewash Station - Water Hammering

05/12/2010 4:46 PM

OK. Sorry, I should have asked more questions to start. Just a few more.

Assumption 1: There is a paddle at the basin, and operating the paddle starts the waterflow out of two fixed diffusers, spraying water into each eye, catching in the basin. This functions correctly; i.e. no hammer.

Assumption 2: There is a flexible hose attached to the riser somewhere near this paddle actuator. This is a body wash. The other end is a squeeze valve with larger diffuser. When you operate the squeeze valve, it functions improperly... the water hammer issue is evident.

OR, are the two functions swapped? OR, do both hammer all the time?

Whichever is the case, it probably is a bad diverter. Assumption #3: If the paddle is open and the water is running, and then you squeeze the valve, the basin wash shuts off. If assumption #3 is correct, a bad diverter valve is the most likely culprit.

If assumption #3 is incorrect, and it hammers all the time... well, it's broke.

__________________
Semper Ubi Sub Ubi
Register to Reply
Active Contributor

Join Date: Mar 2010
Location: New York, the lakeside
Posts: 20
#8
In reply to #3

Re: Eyewash Station - Water Hammering

05/13/2010 7:08 AM

Assumption #1= No. When I push the paddle to start the flow, the chattering or hammering starts.

Assumption #2= No. There is no shower attached.

I am considering adding water hammering arresters on the incoming flow to the eyewash. But what I don't know is if the problem exists around the balancing valve.

Is there a way to test if the problem is at the balancing valve with out replumbing the whole set-up?

__________________
I refuse to succumb to the will of an inanimate object!
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#9
In reply to #8

Re: Eyewash Station - Water Hammering

05/13/2010 9:07 AM

Hello Toomany.

I was leaning away from fluid hammer in the pipes, this due to both hot and cold chattering (I guess) equally. A solid test would be eliminating the eyewash valve and running the water. This test will confirm where the problem is.

It still sounds like the diverter valve in the mixer.

__________________
Semper Ubi Sub Ubi
Register to Reply
Anonymous Poster
#4

Re: Eyewash Station - Water Hammering

05/12/2010 5:12 PM

Maybe you need to install water hammer arresters on both the hot and cold lines. The small column of air in the arrester acts like a shock absorber, since it will compress while water will not.

You can try one of the big-box hardware stores. Here's one manufacturer's info:

http://www.siouxchief.com/Supply/Arresters-And-Trap-Primers/Water-Hammer-Arresters2/Mini-Rester.7R7YG

Register to Reply
Anonymous Poster
#5

Re: Eyewash Station - Water Hammering

05/12/2010 6:41 PM

The appropriate term for this is most likely not 'water hammer'

Strictly speaking, water hammer DOES NOT occur when water is flowing. It only happens when you suddenly stop water flow. What you have is more likely analogous to 'water chatter' in a household that is usually attributed to a faulty washer in the facet. Have you inspected your paddle valve? Do you have a faulty regulator?

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: Eyewash Station - Water Hammering

05/12/2010 9:21 PM

Water hammer can occur when water is flowing. You information is incorrect.

Water hammer can occur any time the flow of water is diverted, or altered as in opening a branch line abruptly, or closing or opening a supply valve. The solution may be the same in either case.

Cheers.

Register to Reply
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#7

Re: Eyewash Station - Water Hammering

05/13/2010 5:40 AM

Try reducing the flow rate through your supply pipe.

__________________
If only you knew the power of the Dark Side of the Force
Register to Reply
Anonymous Poster
#10

Re: Eyewash Station - Water Hammering

05/13/2010 10:04 AM

Kill two birds on a stone:

Swap the ladies room bidet and the eye-wash valves.

You'll make everyone happy.

Yahlasit

Register to Reply Off Topic (Score 18)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#11
In reply to #10

Re: Eyewash Station - Water Hammering

05/13/2010 10:17 AM

Oh, Yahlasit!

Oh, my goodness!

Pretty funny though!

__________________
Semper Ubi Sub Ubi
Register to Reply Off Topic (Score 25)
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#12

Re: Eyewash Station - Water Hammering

05/13/2010 2:04 PM

I had this problem. I fixed it by making a tee fitting on both the hot and cold pipes leading to the eye wash station. (the hot one only went to the overhead shower) From the tee fitting I soldered a short piece of pipe (a couple of hand spans) going straight up, and capped it off. Scraps of pipe are good for that.

It wasn't a water hammer specifically, but some sort of resonant frequency humming in the long pipes, the effect was like a gentle hammering or spluttering during use, and when you closed off the paddle, there was a big hammer like bang.

same easy fix for both problems at once.

Good luck...

__________________
If it was easy anybody could do it.
Register to Reply
Guru
Popular Science - Weaponology - New Member Hobbies - Fishing - New Member

Join Date: May 2007
Location: Aloha or
Posts: 659
Good Answers: 19
#13

Re: Eyewash Station - Water Hammering

05/13/2010 4:16 PM

I thought you could only use cold water in safety showers and eye wash stations to reduce chemical reactivity? I have been definitely told this while working in the semiconductor industry and in college chemistry labs.

Has this changed?

__________________
Closed biased minds are utterly impervious to any factual evidence which contradicts their beliefs
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#14
In reply to #13

Re: Eyewash Station - Water Hammering

05/13/2010 4:25 PM

ANSI/ISEA Z358.1-2009 requires the use of tepid water in eyewash fountains.

Tepid water is defined as 60°F for the lower limit and 100°F as the upper limit.

I am assuming this is the standard in force.

Jim Johnson, chairman of the ISEA Emergency Eyewash and Shower Group and general manager of Encon Safety Product said "By defining a suitable delivery temperature of 60 -100?F, the standard seeks to ensure that the victim continues flushing the affected area to minimize any damage."

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#15
In reply to #13

Re: Eyewash Station - Water Hammering

05/14/2010 8:03 AM

I didn't design it, I just installed it man! All this was in an aircraft hangar, inside the space but near the door. I think people were worried about the hydraulic systems, especially those new fangled artificial fancy designer hydraulic fluids they are using on aircraft today.

The hot water never did actually get to the eye wash station, they went to the shower associated with it. I don't think a single user would ever get to the warm water, there must have been 100 feet of three quarter inch copper pipe! But, presumably, if there was a bunch of people cycling through, they would eventually need the mixed hot-cold. To my admittedly fading memory, they didn't bother mixing the hot and cold for the eye wash station itself.

My only real problem (as usual was political) was to get permission to put the curtain around the shower. The Looie seemed to think it was superfluous but finally I found the requirement in the CCOHS for that too. They don't give a lot of reasons for their decisions.

__________________
If it was easy anybody could do it.
Register to Reply
Member

Join Date: Sep 2009
Posts: 7
#16

Re: Eyewash Station - Water Hammering

05/30/2010 10:16 PM

Toomany,

Solution to your problem is provide an Air Chamber by using tee connection cut one foot of pipe and cap it on top portion the other end connected to tee, then the bottom tee connection for your water supply (either hot or cold) front connection of tee is your water feed to eyewash. The Air Chamber will serve to absorb water hammering. There are also a lot of solution in the market but this one is the cheapest.

Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#17
In reply to #16

Re: Eyewash Station - Water Hammering

05/31/2010 8:43 AM

Um...comment 12....

__________________
If it was easy anybody could do it.
Register to Reply