Paralleling of CBCTs

05/15/2010 11:24 PM

Friends,pls tell me how to give earth fault protection to the 2 runs of cables feeding the same load,using CBCT?

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: PARALLELING OF CBCTs

05/16/2010 12:16 AM

Do i understand you correctly, are both cables from the same source, feeding the same load ?

In such a case, the CBCT should encompass both cables (both are 3φ+N i hope?). Earth fault protection is achieved.

However, if the sources are NOT the same (mains/generator for example), then also, only one source is feeding the load is it not? So the same CBCT will still work, since only one cable will be carrying current at any point in time.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#3
In reply to #1

Re: PARALLELING OF CBCTs

05/16/2010 3:56 AM

They are 2RX3.5CX300sqmm cable from the same source to the same feeder.The CBCT we have cant accommodate both the cables ,as one can imagine the size of the cables......Is it advisable to parallel them to the earth fault relay CDG14?

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #3

Re: PARALLELING OF CBCTs

05/16/2010 9:50 AM

I would advise you to go for three CTs in the busbar and residually connect the ELR.

Register to Reply
Anonymous Poster
#5
In reply to #4

Re: PARALLELING OF CBCTs

05/16/2010 12:31 PM

Nice to see you back sir! Isn't connection will trip on unbalance also???The connection plan we have won't work?pls opine soon..........

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6
In reply to #5

Re: PARALLELING OF CBCTs

05/16/2010 9:12 PM

To provide for unbalance only you do have plug settings in the relay. Don't you? If you still want to have sensitive earthfault protection, you may go for a neutral CT too and connect it too in the residual circuit. Now, the relay wouldn't trip for unbalance, which would be offset by the neutral CT.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#8
In reply to #6

Re: PARALLELING OF CBCTs

05/18/2010 1:13 PM

Won't the scheme we are going to implement work?Pls reply.Is it not practical to connect cbct in parallel?We have no other option for time being.

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9
In reply to #8

Re: PARALLELING OF CBCTs

05/18/2010 9:13 PM

Assume that in one of the cables there is an earth leakage and its CBCT gives an output. Now, if the other cable is healthy, its CBCT will act as a burden to the faulty cable's CBCT and the output of this CBCT(F) will circulate thro the output winding of the CBCT (H) and there will be current division. The earth leakage relay may not receive the current for proper operation and thus protection is compromised.

Though a rare occurrence the above scenario cannot be ignored.

But, I have seen rectangular window type CBCTs for encircling larger cross sectional areas. In the past, I have even encircled bus bars in Unitised Sub-stations with such rectangular CBCTs.

Electrical Expert65

Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#2

Re: PARALLELING OF CBCTs

05/16/2010 2:52 AM

cbct (supply side)+ elr (1 phase n neutral or earth)........elr should be linked to a shunt trip release (MX) Linked to mccb (load side)

__________________
shamith gambhir, electrical engineer
Register to Reply
Active Contributor

Join Date: Dec 2009
Posts: 14
#7

Re: Paralleling of CBCTs

05/17/2010 5:18 AM

Hi

Why can't u treat these two cable as two separate feeders and arrange protection.

RajuS