is K2S2 = I2t (K square S square = I square t) a correct formula for calculating the busbar cross section using short time current value?for example i have 40kA overcurrent for duration of 3 sec for a copper busbar and i want to have the cross section.

if it is a correct formula,what is K??i know its some kind of constant related to insulation and installation type and material etc., consider copper busbar and connected using bolts and nuts.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: short time current withstand calculation for busbars

05/20/2010 5:12 AM

The cross section will decide the thermal withstand capability of the busbar, what about the ability to withstand the dynamic forces due to the asymmetric peak which appears on the first half-cycle ? That will depend on the supports mainly. You may get some useful information here : Schneider-electric ect158.pdf

There are also some threads on CR4, you can browse them too.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: short time current withstand calculation for busbars

05/20/2010 9:20 PM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: short time current withstand calculation for busbars

05/20/2010 9:41 PM

Good link. GA

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Associate

Join Date: Oct 2009
Posts: 47
#4
In reply to #2

Re: short time current withstand calculation for busbars

05/21/2010 7:35 AM

thanks for your information very good link

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

kvsridhar (2); msamad (1); sridharganasen (1)

Previous in Forum: Power calculation   Next in Forum: Root Three in Three Phase Calculation

Advertisement