Busbar Derating

05/25/2010 7:12 AM

I want to use busabr for 800A,

What are the main derating factors should be consider for selection of the busbar.

And what will be the size of the busbarb for 800A

Please give me the answer with all the details and calculations

Rakhi

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Busbar Derating

05/25/2010 9:57 AM

Please check out the many threads in CR4 using the keyword 'busbar'. Here is one for you : Busbar

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#2

Re: Busbar Derating

05/25/2010 12:03 PM
  • is it indoor or out door,
  • plugin or feeder,
  • ventilated or totally enclosed
  • ,copper or aluminium,
  • voltage and frequency rating.
  • is it 3 phase 4 wire system,
  • neutral size half, full or double?,
  • earthing bar size requirement 50% or 100%,
  • run length,
  • ambient temperature,
  • installed at conditioned or non-conditioned area,
  • short circuit rating for 1 sec or 3 sec?,
  • what is the prefered insulation- teflon or resin.,
  • what is requirement of copper purity?
Reply
Anonymous Poster
#3
In reply to #2

Re: Busbar Derating

05/26/2010 1:13 AM
  • is it indoor or out door, - idoor
  • plugin or feeder, - feeder
  • ventilated or totally enclosed - Totally enclosed
  • ,copper or aluminium, - Both
  • voltage and frequency rating. - Voltage 415, Current - 800A
  • is it 3 phase 4 wire system, - 3 Phase , 4 Wire
  • neutral size half, full or double?, - Neutral Half
  • earthing bar size requirement 50% or 100%, - 50%
  • run length, - Max. 4.8 Mtrs.
  • ambient temperature, - 30 Deg.
  • installed at conditioned or non-conditioned area, - Non conditional area
  • short circuit rating for 1 sec or 3 sec?, - 1 Sec.
  • what is the prefered insulation- teflon or resin., - Teflon
  • what is requirement of copper purity? - 0.9
Reply
Anonymous Poster
#4
In reply to #3

Re: Busbar Derating

05/26/2010 3:15 AM

Thats fine. Now, just call any Busbar supplier or manufacturer and give this details. He will give you the correct information as they have standard products for certain current rating.

Reply
Anonymous Poster
#5

Re: Busbar Derating

05/28/2010 1:47 PM

The various derating factors are K1-temperature rise,K-2 alloy impurity,K-3 altitude

K-4 thermal capacity variations for different layout(ref.DIN43670),K-5 electrical load capacity for different lay out.

Besides there is up rating factor also like using non metallic black matt finish paint( 20% uprating for AL), different bus arrangement ( up rating up to 18%)

Hence all these are to be considered to arrive at actual size in BB design

You consider 0.8 A / sqmm for Al and 1.2 A /sqmm for CU for simple calculation.

So for 800A (AL bus, 100x10 mm Al )and for (CU bus,75x10mmCU)

Reply