VFD

05/28/2010 9:24 PM

I need an explanation of VFDs. I mean its inbuilt, how it works and how its output voltage is controlled.

Register to Reply
Pathfinder Tags: VFD
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: vfd

05/28/2010 11:13 PM

VFD's are built using electronics, they work real good and the output voltage uses feedback control. Don't expect to hit the knowledge lottery here, you must put in some effort to learn. GA?

Register to Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: vfd

05/29/2010 6:20 AM

Your question looks like explanation notice to subordinates.

"Sorry sir,...i will submit the explanation very soon."

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#3

Re: vfd

05/30/2010 12:55 AM

VFD or variable frequency drive... not variable voltage drive. The voltage is usually constant, I've not come across one that has a variable voltage.

How it works.... simple version: AC incoming is rectified to DC, then inverted to AC thru the IGBT's which in turn gives you the Hz output at a predetermined voltage.

Google it.. then if you have questions please come back

__________________
The square root of nothing is what you make it!
Register to Reply
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#4
In reply to #3

Re: vfd

05/30/2010 2:55 AM

When the frequency is reduced in a vfd the VOLTAGE will be reduced proportionally. This is done usually by the V/F limiter.Otherwise the core flux density will increase resulting in excessive core losses.

__________________
Better not count the cent if the risk is many many dollars.
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#5
In reply to #4

Re: vfd

05/30/2010 5:11 AM

Yes I know that.... the question was how is the voltage controlled, the voltage is not its the Frequency that is raised or lowered depending on the speed required, the voltage change is direct result of the Hz change, however as you say there are limits to be set and I did not want to try and give the OP a master class in VFD's without him doing some work. It sounds to me that this is a college class project and while it could be looked at as "research" asking CR4 is an easy was of getting research done

__________________
The square root of nothing is what you make it!
Register to Reply
Commentator

Join Date: Mar 2009
Location: Georgia mountains
Posts: 64
#6
In reply to #5

Re: vfd

05/30/2010 6:26 AM

I agree with you britch, but I think it is OK to say that vfd can be used to control mechanical systems by adjusting the frequency and voltage supply to typically a 3 ph electric motor. As the rotor responds to the rotating magnetic field created work is done. If the frequency gets too low or the rotor does not comply with the magnetic forces, the magnetic circuit could begin to saturate creating losses and higher than necessary current in the motor windings. Most vfd's reduce the drive voltage below a given frequency such as line frequency. Often vfd's are used with some kind of feedback, but they can run open loop also.

Regards,

Luther M

__________________
There are old pilots and there are bold pilots, but there are no old bold pilots.
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#7
In reply to #5

Re: vfd

05/30/2010 9:55 AM

It sounds like by controlling the frequency of an oscillator the resultant output voltage will follow! Similar to a simple light dimmer application, by varying the oscillator frequency, one can control the firing angle(s) of thyristor(s), such as triac or SCR, which will determine the amount of time this thyristor(s) will be triggered conducting (ON state). This basic AC control concept has a lot of different applications, both in single phase and polyphase AC controls. When incorporated with a feedback loop, it can also be applied affectively in magnetic amplifier applications such as ferro-resonant type of voltage stabilizers. Above statements were from an old personal experiences.

__________________
vsar
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#8
In reply to #7

Re: vfd

05/30/2010 12:45 PM

very quickly, light dimmers change the voltage, not the frequency, while VSD, by inverting the DC bus voltage gives you the Hz you require, the voltage of the sine wave will follow. But if you are going into detail, then you MUST talk about total Harmonic distortion (THD), short circuit ratios, motor output and a whole mountain of other things that the OP has not even heard of.

However if the VSD maintains a Volts to Hz ratio the the HP output of the motor changes, as well as the motor RPM increasing or decreasing.

With modern VSD/VFD in the application I use them, we then feed the VSD output into a Step-up transformer to give 2000 volts plus for the ESP's, then we also have to take into consideration the transformer ratio too! plus the additional harmonics...

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#11
In reply to #8

Re: vfd

05/31/2010 8:00 AM

Light dimmers , motor speed controls, etc are all pretty much the same. The main difference is the type and output power handling capacity required for any given application. This will also determine what type of electronic component that will be driven by the VFO to much that particular application. The key is the variable frequency oscillator that any end user will or can adjust depending on the desired effect. The variations in the oscillator frequency will in turn can be converted into voltage, current, etc. necessary for any given application. A typical application example, The VFO frequency variations can also be translated into an equivalent varying small DC voltage that can be used to effectively saturate the core of a transformer, (most linear portion of the hysteresis curve) which in effect can control its magnetic characteristics via the alteration of the magnetization curve.

__________________
vsar
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#12
In reply to #11

Re: vfd

05/31/2010 9:33 AM

In reply

There is no way that dimmers and speed controllers are the same...see below

"Dimmers are devices used to vary the brightness of a light. By decreasing or increasing the RMS voltage and hence the mean power to the lamp it is possible to vary the intensity of the light output. Although variable-voltage devices are used for various purposes, the term dimmer is generally reserved for those intended to control resistive incandescent, halogen and more recently compact fluorescent (CFL) lighting".

More specialized pulse-width modulation equipment is needed to dim fluorescent, mercury vapor,solid state and other arc lighting.

There are not many application for a VFD (not VSD) in lighting control, only in the theater because of the heat

"Modern dimmers are built from silicon-controlled rectifiers (SCR) instead of potentiometers or variable resistors because they have higher efficiency. A variable resistor would dissipate power by heat (efficiency as low as 0.5). By switching on and off, theoretically a silicon-controlled rectifier dimmer does not heat up (efficiency close to 1.0)".

I quote from; see link

http://en.wikipedia.org/wiki/Dimmer

Dimmer: decreases or increases the RMS voltage and hence the mean power to the lamp it is possible to vary the intensity of the light output.

VSD or VFD: converts AC to DC then back to AC using IGBT's to produce the required Hz and voltage to control the RPM of an AC asynchronous motor, usually 3 phase.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#13
In reply to #12

Re: vfd

05/31/2010 10:54 AM

Of course! since they differ only in names due to differing final applications! The circuit design approach remained the same since you'll need a VFO as the INITIAL stage in your control mechanism. And depending on the chosen type of output requirement, it may be a proportionally varying frequency, voltage, or current, as well as the amount of power capacity required. The Driven or final stage component, (IGBTs, IGFETs, thryristors, etc.) will also be determined based on the type output required! This basic and general approach in circuit designs is applicable to both AC or DC, analog or digital applications. As simple as a light dimmer, to UPS' or to a more complex power regulation applications, The VFD in question is only one of those different applications requiring an initial VFO. I just don't limit myself on different terminologies since ultimately they will be determined by their final usage or application and labeling when marketed!

__________________
vsar
Register to Reply Score 2 for Off Topic
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#14
In reply to #13

Re: vfd

05/31/2010 3:10 PM

I think you are either

1. Getting your VFD's and VFO's mixed up

2. You don't know the difference between a VFD and a VFO

3. or are just trying way to hard to impress the forum by telling everyone about VFO's, that do not exist in a variable frequency drive.

I have looked for VFO's and the answers I got is as follows

"A variable frequency oscillator (VFO) in electronics is a oscillator whose frequency can be tuned (i.e. varied) over some range.[1] It is a necessary component in any tunable radio receiver or transmitter that works by the superheterodyne principle, and controls the frequency to which the apparatus is tuned."

could you be confused by a Voltage Controlled Oscillator?

"A voltage-controlled oscillator or VCO is an electronic oscillator designed to be controlled in oscillation frequency by a voltage input. The frequency of oscillation is varied by the applied DC voltage, while modulating signals may also be fed into the VCO to cause frequency modulation (FM) or phase modulation (PM); a VCO with digital pulse output may similarly have its repetition rate (FSK, PSK) or pulse width modulated (PWM)."

Applications of a VCO

VCOs are used in: * electronic jamming equipment * function generators, * the production of electronic music, to generate variable tones, * phase-locked loops, * frequency synthesizers used in communication equipment.

There is one application that is not mentioned, in EVERY VSD there is a crystal to give the snubber firing boards that control the IGBT's their reference to work from

Voltage-Controlled Crystal Oscillator as a Clock Generator: A clock generator is an oscillator that provides a timing signal to synchronize operations in digital circuits. VCXO clock generators are used in many areas such as digital TV, modems, transmitters and computers.

As a new member to the forum, you need to stay on tack with the OP question, you have managed to work me away from it, added to the OP's confusion and proved that you can confuse the issue with unrelated information that really has no real value to the OP. The best and only answer that explained to the OP in detail was from jmueller, after that nothing else required.

Quoted texts are from:

http://en.wikipedia.org/wiki/Variable-frequency_oscillator

and

http://en.wikipedia.org/wiki/Voltage-controlled_oscillator

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Good Answer
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#16
In reply to #14

Re: vfd

06/01/2010 9:23 AM

I concur to all given circuitry details for a VFD! Earlier comments given are conceptual ideas on how instrumentation controls, its design mechanisms can be approached or looked at! Actual circuit similarities as well as differences will depend Only on the particular chosen application! It is very general and open ended! As these 2 cents of mine were taken from old designing experiences back in the mid 1960s, will put me way far from being either !! - I'm dead sure I'm neither.

__________________
vsar
Register to Reply Score 1 for Off Topic
2
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#9

Re: vfd

05/31/2010 12:02 AM

Sicc_Mani,

Let me try: A typical VFD has 4 parts or sections:

  1. The incoming power section has fuses and rectifiers to convert the line's AC power into DC.
  2. The DC bus section has the capacitors and other components to filter out noise so this DC bus voltage is stable. It usually also has a contactor (big relay) to shunt power from the DC bus to a BIG resistor if the VFD is taking power back from the motor (I won't explain how this works, but it can be done).
  3. The inverter section uses six IGBT's (Insulated Gate Bipolar Transistors), to pass pulses of this DC voltage out to the motor in a way that appears (to the motor) to be the frequency and voltage needed to run the motor at its desired speed. This will be discussed below.
  4. The control section has the brains and memory needed to monitor the health of the VFD and motor and control the switching on/off of the IGBT's as needed to match the input commands from the keypad or control terminals.

Most VFD's (but not all) have an oscillator clock that is used to count when to turn each IGBT on or off. The frequency of this clock is called the carrier frequency, and can be changed by the user--higher means the motor is a little quieter, but the drive works harder (is less efficient).

  • For my discussion, let's assume the carrier frequency is set to 5000 Hz (if you are in an area that has 50Hz power) or 6000 Hz (if you are in an area that has 60Hz power). Thus, for each cycle of the utility's power, you have 100 possible times the IGBT's can be turned on or off. Since an AC voltage waveform is (mathematically described as a) sine wave, it is positive for one half of each cycle and negative for the other half.
  • Lets assume I turn an IGBT on positive for one pulse of the carrier frequency and turn an IGBT on negative for one pulse of the carrier frequency exactly 50 pulses later, and repeat this. Lets assume (correctly) that this pulse gets filtered a little by the time it reaches the motor. The motor will be seeing a 50 (or 60) Hz signal but at a low voltage.
  • Instead of the above, lets assume I turn the IGBT's on positive or negative for ten pulses of the carrier frequency (positive for 10 out of 50 and negative for 10 out of 50). Now the motor will be seeing a signal with the same frequency but a higher (average) voltage.
  • Lets change things again. Now we turn the IGBT's on positive for 10 out of 150 and negaive for 10 out of 150 pulses of the carrier frequency. The motor will be seeing a signal with the same (sort of) voltage, but at a much lower frequency.
  • Now, let me turn the IGBT positive: on-1 and off-4, then on-2 and off-3, then on-3 and off-2, then on-4 and off-1, then on-14 and off-1, then on-3 and off-2, then on-2 and off-3, then on-1 and off-4; then repeat this same pattern for negative. The motor will be seeing a voltage that rises to a positive and then goes to a negative peak and returns to zero. The frequency is now 50 (or 60) Hz but the voltage to the motor is rising and falling like a sine wave.

Do you see how turning the IGBT's on positive and negative for varying portions of time can make the motor act as if it is receiving power with a variable frequency and variable voltage? All you have to do is put all the logic into the control section of the VFD so it will turn 6 IGBT's on and off as necessary to provide this variable output voltage and frequency. But, you also need a means for displaying the status of the drive to the user, and monitoring the circuits for safety and any overload problems, and ..., and..., and....

--John M.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Sep 2006
Location: New Jersey, USA
Posts: 178
Good Answers: 8
#15
In reply to #9

Re: vfd

06/01/2010 6:42 AM

I agree this is a pretty good explanation but I would like to add a few things:

For Part 1: The rectifier can be passive (diode bridge) or active SCR's. If passive there will likely be a pre-charge resistor and a bypass contactor. This is for start-up to protect the rectifiers when trying to charge the capacitors mentioned in #2. Once the caps are above some threshold voltage the bypass contactor engages removing the pre-sharge resistor from the current path. SCR's can just vary their firing angles to accomplish the same result.

Part 2: Dynamic braking is done via a "Chopper" which is usually a transistor of some type not a contactor.

The Output of the IGBT's is usually a "PWM" output. Some VFD's allow you to change the carrier frequency of the PWM. The higher the frequency the greater the switching losses on the IGBT's but the quieter the motor will operate which can be a big deal, particularly in HVAC applications.

In contrast to a light dimmer the VFD is different in that it has the "Front-End" to convert the incoming voltage to DC. It also runs at much higher carrier frequency. A Light Dimmers carrier frequency is line frequency where as a VFD can be anywhere from 2-12KHz or more.

Shawn

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#17
In reply to #15

Re: vfd

06/01/2010 9:40 PM

Shawn33,

Your additions are helpful. Depending on the application, slowing the driven load can be as simple as a controlled decrease in the output voltage and frequency while the driven load takes away the stored inertial energy in the motor and load. Or, if the stored inertial energy is more than can be taken away by the load in the time desired for stopping, then the VFD's design has a way to take back the energy. This results in adding to the voltage in the DC bus section. The VFD's have two design methods for keeping the charge on the DC bus from getting too high--either dump it to a resistor load bank outside of the drive (by SCR's as you noted), or (on line regenerative types of drive designs) put it back onto the "incoming" power line.

In my earlier post I noted that "most" drives have a preset (but user-adjustable) carrier frequency. It is heard as a singing from the motor's laminations. I have worked with a few that switch the IGBT's on and off without the use of a clocked carrier frequency. They were very quiet.

Regarding typical light dimmers, they have no DC bus and output a variable voltage at the same frequency as the incoming line frequency.

--JMM

Register to Reply
Associate

Join Date: Jan 2007
Posts: 35
Good Answers: 1
#10

Re: vfd

05/31/2010 7:39 AM

VFD is variable frequency drive. This is used to vary speed of the motors by varying the frequency. However correspondingly the voltage will also get changed proportionaly. The referred motors are used for driving the centrifugal drives like fans/pumps. when these drives are operated on part load due to process requirement, the overall efficiency of the process is becoming low. However if we operate at the optimum speed without killing developed pressure by the drive, the eficiency is not affected. Further the starting current will also be reduced considerably (approximately 1.5 to 2 times) thereby reducing burdon on distribution system (normally directon line starting will draw current six times full load current). We understand the payback period for additional cost involved in providing VFD is 12 to 18 months.

R.Thiyagarajan

Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); Anonymous Poster (1); brich (5); Jans (1); jmueller (2); Luther M (1); rajant_2001 (1); Shawn33 (1); vsar (4)