Anonymous Poster

Calibration Range for Dp Transmitter

05/30/2010 8:00 AM

I want to know wht ll be the calibration range for a dp type level transmitter where medium liquid is process water and the measuring range is 0-5800 mm inside a closed vessel.

specific graviy of capillary fill fluid is silicon dc200 =0.94 and process water 1

the transmitter is installed at the base high side tapping point ( no elevation or supression)

Could u kinldy let me know the formula for calculating the reqd calibration range. The calibration range which is mentioned to me in the datasheet is 0-569mbar. But I am unable to produce this result by my calculation.

thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Oct 2007
Location: Canning Vale Western Australia.
Posts: 160
Good Answers: 7
#1

Re: Calibration Range for Dp Transmitter

05/31/2010 6:18 AM

The transmitter must be fitted with both legs connected to the vessel. The low side of the TX should connect to the top of the vessel via a wetleg and must remain full of process (this gives the reference to full level). The high side of the TX is connected to the bottom of the vessel. Your calibration range will be -5800mm H2O to 0mm H2O.

__________________
I attend work so my dogs can have the good life.
Reply
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#2

Re: Calibration Range for Dp Transmitter

05/31/2010 6:01 PM

Hi,

The formula is P=h x s.g.

If h=5800mm in others words the distance between the bottom tap(high side) and the top tap(low side) is 5800mm then P=5800X0.94 equals 5452 mm of water since this pressure is being applied to the LOW side then this value will be negative.

-5452mm of water is your ZERO or LRV, it can be verified by installing the transmitter legs on their corresponding places and opening them to atmosphere.

To calculate the URV, P=5800mmX1 equals 5800mm of water so to have 100 % level you are going to go 5800mm of water to the positive side starting at -5452mm of water.We do the calculation -5452+5800=+348mm of water.

LRV=-5452mm of water

URV=348mm of water

Span=5800mm of water

Personally when using capillary transmitters I don't figure my zero using the formula I rather install the transmitter and vent both legs then connect my communicator to find the pv value.

I hope this help you I am having problems putting my thoughts in words.

Have a nice day!

__________________
"The older I get -The better I was"
Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#3

Re: Calibration Range for Dp Transmitter

05/31/2010 10:18 PM

The conversion from mm water column to mbar is:

5800 mm water = 568.78 mbar, which is where the range of 569 mbar comes from.

If the units on the transmitter include mbar, then

LRV -5452 mm of water = -534.65 mbar

URV 348 mm of water = 34.12 mbar

The span from -534.65 to 34.12 is 568.77 mbar

Reply
Anonymous Poster
#4

Re: Calibration Range for Dp Transmitter

10/02/2010 12:13 AM

Dear

569mbar is equivalen with 5802.185 mmh2o(mmwater)

now I give code for you information,heigh water ( h ) 5800 mm.sg process (sg1 ) 1,sg capillary ( sg2 ) 0.94.heigh of capillrary on lowside (d) 5800 mm

span = h x sg1

= 5800 mm x 1.

= 5800 mmh2o

zero = d x sg2

= 5800 x 0.94

= 5452 mmh2o

Range = -5452 to (5800 -5452 ).or -5452 mmh2o to 348 mmh2o

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Carl_E (1); Doggoneit (1); wrenchpuller (1)

Previous in Forum: LCR Meter Readings   Next in Forum: Gauge Cock vs. Manifold

Advertisement