High and Low Grid Frequency and Voltage

05/31/2010 4:20 AM

Please help,

While running the STG in parallel to the grid,

  1. If the unit is at full load and the grid frequency goes to 51 hz. what will be course of action for the station incharge to save the machine and the unit.
  2. If the total power is sold in open access then what will be course of action.
Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: High and low Grid frequency and voltage

05/31/2010 9:59 AM

I have just three comments.

  1. Eschew Obfuscation
  2. CRIMINAL
  3. Refer to your textbook on circuit analysis to derive the appropriate equations. Examine what will happen as ω varies 15%. If you haven't had this class....
__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Active Contributor

Join Date: Jan 2010
Location: Bharuch , Gujarat , India
Posts: 17
#2

Re: High and low Grid frequency and voltage

05/31/2010 11:31 AM

Dear friend , when STG parallel with grid we can not change grid frequency .please check nearest sub station frequency set point at which level you have to set your STG at that set point . when you export power that time if grid tripped in high frequency your STG TRIPPED due to high frequency and your STG will be safe ok from jayesh sathwara

__________________
jayesh b sathwara
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: High and low Grid frequency and voltage

05/31/2010 11:39 AM

Ok, could somebody explain what STG does while paralleling the grid. Besides sounding cool.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#4

Re: High and low Grid frequency and voltage

05/31/2010 11:53 PM

I presume that STG is Steam Turbine Generator (Turbo Generator). Please go through the Operation Manual supplied by the Generator manufacturer. That gives the limits of Voltage, Frequency variation (and also the combined variation) within which the the set can operate. Normally any set would operate satisfactorily for 51Hz at rated voltage.

Reply Score 1 for Good Answer
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#5

Re: High and low Grid frequency and voltage

06/01/2010 12:33 AM

dear Guest Welcome to the forum If your STG is connected to Grid, and the frequency of grid go to 51 hz ( i assume you were running at 50hz), than suddenly your STG stop delivering power and receive a huge amount of reverse power, as the control of STG RPM is usually slow, the only measure you can take to save your unit is to isolate it immediatly from the grid question 2- please resubmit in different editing, I didnt understand it Regards

__________________
dont say it, write it
Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#6
In reply to #5

Re: High and low Grid frequency and voltage

06/01/2010 1:16 AM

Reverse cannot flow from the grid till the prime movers is supplying the power. Further as long as the generator is connected to the grid, generator cannot run at speed other than that of the grid. If the grid frequency increases due to load throw off then remaining load will shared by the units connected to the grid. 51 Hz should not be a cause of concern (assuming it is a 50 Hz system).

Reply
Participant

Join Date: May 2010
Posts: 2
#8
In reply to #6

Re: High and low Grid frequency and voltage

06/02/2010 2:20 AM

Dear Sir, the grid freq. is 51 hz and voltage is 139 kv, can over fluxing occur. Though we reduce the loading, the grid condition is same. so I think it is not good to reduce load on monitary basis. else what to do in such condition. Pl. suggest

Reply Score 1 for Off Topic
Anonymous Poster
#7
In reply to #5

Re: High and low Grid frequency and voltage

06/02/2010 1:58 AM

Dear Sir, thanks for your valuable comment.

for my question 2, the trip value for the generator is 52 Hz ( as we are running on 50 Hz) we have to pump power in to the grid though it is saturated and the turbine RPM also goes high upto 5090. If there is any fluctuation of voltage or frequency in the grid this can lead to station tripping. but we cannot isolate the STG form grid as we r exporting power in open access to the third party. so in this condition what will be the safe action.

Regards,

Reply Score 1 for Off Topic
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Ashish Dhiran (1); jayesh100375 (1); Le_Noble (1); pcchatur (2); redfred (2)

Previous in Forum: CT Burden and Class   Next in Forum: Current Density of Electrolytic Aluminum Flats

Advertisement