Interposing Relays

06/01/2010 4:33 AM

What is the sole purpose of interposing relays and where can it be used?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Interposing relays

06/01/2010 5:03 AM

When the power which needs to be handled exceeds the capacity of the product in question, an interposing relay is used.

An example - let us say you have a very large motor to be switched on, and the contactor which should switch on this motor is say 800A. Its electromagnet will require possibly 1kW of power to switch on. This cannot be handled by the small pushbutton that is on the front panel of the starter. So, an interposing relay is used, which can handle the power of 1kW or more, and the pushbutton is wired to switch on the interposing relay's electromagnet, which should be very small.

This is just one application, there are many others, you can search on google.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 2)
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Interposing relays

06/01/2010 5:32 PM

Interposing Relay is the auxiliary relay which is used to isolate the two different systems (such as high current and low current or 24V control and 120V control or AC voltage and DC voltage etc.) in the control circuits. For example, if the motor's contactor coil voltage is 120V AC but PLC signal is 24V DC and it is required to operate the motor from the PLC signal, an interposing relay of 24V DC is used in the PLC circuit loop and its dry contact is wired in the 120V AC circuit to operate the motor. Its use is more common in between the instrument system (PLC or DCS) and the electrical system. However it is also used within the electrical system as well. It isolates the two different systems and so it is also called isolating relay. Some people think it couples two different systems and call it coupling relay.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)
Associate

Join Date: Mar 2010
Posts: 28
#5
In reply to #1

Re: Interposing relays

06/24/2010 4:54 PM

Dear Sir,

we are using in incomers of 6.6kv breakers. wat might be the exact purpose

please explain me sir

Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Interposing relays

06/24/2010 8:18 PM

Can you explain the circuitry a little more please ?

Are there interposing relays in a 6.6 kV incomer CB? What are its main contact connections and coil voltage ?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Interposing relays

06/01/2010 5:41 PM

I also use them to reduce MTTR (mean time to repair). In electronically controlled systems, any relay contact in a PLC or other I/O device is going to wear out over time. If you use an interposing relay, the output relay inside the I/O device can last virtually forever, and a plug-in interposing relay can be replaced in a matter of seconds.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Associate

Join Date: May 2010
Location: RSA
Posts: 33
#4
In reply to #3

Re: Interposing relays

06/02/2010 1:30 AM

Thank you guys, these replies opens my eyes a lot.

The reason I asked it is because I have a demand meter that is connected with relays so that the meter can register 1kwh after every 10 pulses or so.My understanding so far it is that, the relay work hand in hand with the meter pulses in order to read 1kwh and 1kva so as to register the info in the consumer's data logger.

This was done because the client needed back-up transparency concerning his consumption and to get the load profile etc.

Should you have more info concerning direct application of interposing relays and its connections, please post.

The other method used to achieve the same results is with the interposing CT's.

Reply Score 1 for Off Topic
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

JRaef (1); kvsridhar (2); msamad (1); venu kodeboyina (1); WisdomJD (1)

Previous in Forum: Heat in Motor   Next in Forum: Cost Curves for Hydrogenerators and Hydroturbines

Advertisement