Anonymous Poster

NGR

06/02/2010 7:36 PM

Dear memebers,

we are supplying power to grid through 69 MVA step up transformer , it is grounded. Our generator (15 MVA) NGR is closed only at the time of synchronisation. after synchronisation we open the NGR breaker

can anyone explain this whether we can open the genrator breaker or not

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: NGR

06/03/2010 2:20 AM

why do you want to open the breaker? for any maintenance inside the breaker?...switch off generator and open.

Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2008
Posts: 24
#2
In reply to #1

Re: NGR

06/05/2010 12:26 AM

Dear GYEST.

U should closed the breaker if u are in need for the generator to be a (stand by unit)

Reply
Active Contributor

Join Date: Jul 2009
Posts: 17
#3

Re: NGR

06/05/2010 5:57 AM

You should not open NGR after synchronisation with GRID to avoid stator earth fault but if you are running multiple genstes than in that case you may opt for switching on one only and reming are off to avoid tripping on circulating current..

Reply
Participant

Join Date: Jun 2010
Posts: 1
#4

Re: NGR

06/10/2010 1:58 AM

if you have more than one generator at that time ony one ngr keep in line other are should be disconnected after synch. of generator

Reply
Commentator

Join Date: Jan 2010
Posts: 73
Good Answers: 1
#5

Re: NGR

06/12/2010 9:13 AM

NGR is primarily installed to protected a certain equipment against ground faults.. you should take note the single line to ground fault during the time your generator is supplying the grid..

when the fault (ground faults occur in the gen bus), the NGR will lessen this current and thus also lessen the fault current in the stator thereby protecting your generator stator..

there are also other reasons you do such a thing for that, provide us with the generator configuration transformer configuration, and all system configuration.

Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); DRK (1); hkian (1); Noorirm (1); pradiplimbachia (1)

Previous in Forum: How to Calculate Line Amps to kW 3-Phase 380V   Next in Forum: Simple timer to control liquid flow

Advertisement