MCCB and MCP

06/07/2010 8:49 AM

Greeting Fellow Engineers and Seniors,

With respect to the LV MCC and DOL starting. Why is there a need to use:-

Contactor, MCP, MCCB, Auxilary Relays, Control CBs etc to protect the motor (lets say 3 kW).

Wouldnt a MCCB with a contactor be suffice to help protect and run the motor (Assuming DOL Starting). Instead were using MCP, Relays, control CBs...Could any one elaborate their specific use.

I hope to hear positive responses from you.

Regards,

Knowledge builder

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: MCCB AND MCP

06/07/2010 9:56 AM

Dear guest,

A simple starter is enough. What it will have are:

  • A short-circuit protective device (SCPD) which may be a Fuse-switch (SD+F or SDF) or an MCCB
  • A contactor
  • A thermal overload relay with phase-loss sensitivity

In an MCC, you may be using other devices like auxiliary contactors for signalling or interlocking purposes. Assuming by MCP you mean an electronic single-phase preventor, it may not be necessary if the phase-loss sensitivity of the thermal overload relay is adequate. Most relays available in India are good enough. (if MCP means something else, please let me know)

As to MCCB+Contactor being enough, the MCCB standard overload characteristic is usually not close enough to give good motor protection if it is a thermal/magnetic one. The recently available microprocessor trip units may be adequate, but at 3kW level, it will be too expensive. Better use the thermal relay.

Moreover, the normal MCCB does not provide phase-loss protection.

Hope this much helps for now, i am sure you will get many more responses which will help increase your knowledge.

If you register as a user on CR4, and everyone knows which is your country, you are likely to get more and appropriate responses.

Good luck.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 3)
4
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: MCCB AND MCP

06/07/2010 10:42 AM

To add to the fine answer given by Mr. Sridhar:

i) MCCB is capable of breaking higher currents than motor overload currents, which could conveniently be handled by the contactor.

ii) Also, the electrical life of MCCB is much less when compared to the electrical life of the contactor.

iii) If you use a thermal overload relay and wire it up to trip the contactor for motor overlods, you loose one out of say, a few lakh electrical operating cycles of the contactor.

iv) If you instead use the thermal element of the MCCB to respond to motor overloads, during motor overloads, you loose one out of a few thousand electrical operating cycles of the MCCB.

v) Now, which one would you prefer? One lakh minus one or one thousand minus one?

vi) Moreover, as told by KVS, the thermal element in the MCCB more tuned for feeder protection and hence may not offer fine overload protection required by motors.

vii) Also, you cannot have an effective single-phasing protection with the MCCB Thermal element, whereas the same can be had from an external overload relay if it is of the phase-loss sensitive type (Double slide mechanism)

viii) The thermal element in the MCCB is not compensated for ambient temperature variations. Hence, due to ambient temperature variations, the trip times would not be consistent. Whereas, with an external thermal overload relay one can have a compensating mechanism for ambient temperature variations, so that the trip time is consistent, irrespective of the ambient temperature cpnditions.

Hope I have added flavour to KVS answer.

Reply Good Answer (Score 4)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: MCCB AND MCP

06/07/2010 10:59 AM

Yes, excellent ! GA to you

i had forgotten the ambient compensation .. for God's sake! i am getting senile.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Score 1 for Good Answer
Associate

Join Date: May 2009
Posts: 40
Good Answers: 1
#7
In reply to #2

Re: MCCB AND MCP

06/07/2010 11:08 PM

can i know your mail id and company name where you are working............

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#12
In reply to #7

Re: MCCB AND MCP

06/08/2010 9:37 AM

I am fully aware of the perils of disclosing my mail ID is an open forum like this. However, if you want to communicate with me, kinldy do so thro this forum's mailbox. I will then definitely inform you my mail ID and my current employer.

Reply
Associate
Engineering Fields - Electrical Engineering - New Member

Join Date: Jun 2010
Location: IEC Domain
Posts: 43
#4

Re: MCCB AND MCP

06/07/2010 1:00 PM

Thank you for your answers. You have removed my confusion. Thank you once again.

P.S I have registered as per your advice.

Regards,

DG

__________________
The Crazy Man Talks and The Smart Man Understands
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: MCCB AND MCP

06/07/2010 1:06 PM

i am very happy that you have got what you wanted, and also to see your registered 'handle'. i am sure you will find CR4 an outstanding forum to learn something new everyday, not to mention the large intellectual power available to solve any problem that you may encounter in your career. Good luck and God bless

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Associate
Engineering Fields - Electrical Engineering - New Member

Join Date: Jun 2010
Location: IEC Domain
Posts: 43
#6
In reply to #5

Re: MCCB AND MCP

06/07/2010 1:11 PM

Thank you Sir for your blessings and warm wishes. I look forward to learning new things.

__________________
The Crazy Man Talks and The Smart Man Understands
Reply Off Topic (Score 6)
Associate

Join Date: Dec 2007
Location: Kochi, Kerala, India
Posts: 27
#8
In reply to #4

Re: MCCB AND MCP

06/07/2010 11:22 PM

I feel it as good to add the following points also in this moment.

MCB - Miniature Circuit Breaker - it is having a preset current rating - In India I think it is available up to 80A (have to check, whether higher rating available)

MCCB - Moulded Case Circuit Breaker - It is having current setting arrangement, by which you can set to your required rating. Also, MCCBs are available with preset factory rating like MCBs.

Other Circuit Breakers are ACB, VCB, etc. using for higher current ratings.

There are Switch Fuse Units (SFU), which are replaced by the Circuit Breakers. The Circuit Breakers are having higher breaking capacity (kA) than SFUs. So, in such required designs the breakers are preferable. But, the fuses of the SFUs are sharp in the breaking of the circuit in the exactly designed value than the breakers. So, in such other required situations we move towards the conventional fuses.

(Hope others will elaborate what I explained above)

__________________
Assistant Electrical Inspector, Govt. of Kerala, India
Reply Score 1 for Good Answer
Associate

Join Date: Jun 2010
Location: INDIA
Posts: 27
Good Answers: 1
#9

Re: MCCB and MCP

06/07/2010 11:40 PM

IT DEPENDS ON THE SEVERITY OF THE APPLICATION.IF YOU GET A MCB WITH VARIABLE CURRENT SETTING FOR THERMAL OVERLOAD IN THAT CASE MCB+CONTACTOR OPERATION IS POSSIBLE.

OTHERWISE ALSO IF YOU ARE APPLYING mcb WITH c TYPE RELEASE,THEN UPTO 3kw mcb +THERMAL OVERLOAD IS APPLICABLE.

THE ONLY THING IS THAT FOR THE APPLICATION WITH mcb YOU CANNOT HAVE A PUSHBUTTON START,AND YOU HAVE TO START /STOP WITH mcb ONLY.

IF YOU HAVE A mcb WITH cONTACTOR THEN YOU HAVE A COMPLETE AUTOMATIC PUSHBUTTON START AND STOP ALONG WITH MOTOR PROTECTION ALSO.

IF YOU DONOT PROVIDE CONTACTOR AND PUSHBUTTON STATIONS YOU CANNOT HAVE A ELECTRICAL START AND STOP/TRIP DURING PROTECTION RELAY OPERATION.

ADDITIONALLY THERE ARE CERTAIN ELECTRICITY RULES AS PER IEC/OR LOCAL BODIES THAT PROHIBIT STARTING AND STOPPING OF MOTORS DIRECTLY THROUGH MCB .

OVERALL MCB GENERALLY USED AS A SHORT CIRCUIT PROTECTION. I>>,WHEREAS THE THERMAL OVERLOAD PROTECTS ONLY I>IE 51,AND PREFERABLY NOT TO BE USED FOR MOTOR STARTING DUTY.

__________________
S BHATTACHARYA
Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#10

Re: MCCB and MCP

06/08/2010 12:57 AM

Lots of interest in this thread. Good. However, some clarifications...

For example,

  • fuses of even 300kA SC capacity are available.
  • Contactors have a life of millions of operations. MCBs and MCCBs have a few thousands. Contactors are 'controlgear' devices, they have no protection function. MCBs and MCCBs are specifically protective devices, to use them to switch on and off motors is not a good idea.
  • Every time a short circuit happens, the fuse blows, and needs to be replaced. The protection is as good as new. If an MCB or MCCB trips on SC, we reset it and switch on again. While the MCCB may be ok to carry rated current after O-CO-CO, there is no protection thereafter. And in a real-life situations, there is no way to know how many short circuits and what current level have happened.(with modern microprocessor relays, some memory is there, still...) The debate of Fuse vs MCCB has been happening for decades, and is never going to be over
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Member
United States - Member - libertas ignigena Engineering Fields - Electrical Engineering - libertas ignigena Popular Science - Cosmology - libertas ignigena

Join Date: Sep 2008
Location: Houston, TX
Posts: 8
Good Answers: 1
#11

Re: MCCB and MCP

06/08/2010 9:30 AM

One more point. MCP is for "motor circuit protector." It will have only magnetic trip as it depends on DOL starter for thermal protection. Smaller circuit breakers are likely used for protection of smaller control or aux circuits that require thermal and magnetic protection appropriate to the circuit size.

__________________
Artificial intelligence can not defeat natural stupidity.
Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#13

Re: MCCB and MCP

06/08/2010 12:48 PM

Sir,

I also welcome you to CR4. Additional information/clarification:

  • Short circuit protection for the motor and its supply wiring is from the MCCB or MCP or fuses.
  • Single phase protection is only available from devices designed specifically for this function, such as IEC style overload relays.
  • Running overload protection can be supplied by a set of fuses or a MCCB if either of these are sized very close to the motor's running current. In the USA, the National Electrical Code recognizes this and provides the maximum percent you can add to the motor's Full Load Amps. In your country, this may be allowed, but I do not know your codes. In some cases, running overload protection may be supplied by internal overload protectors embedded within the motor windings. For very large motors, there will be thermal sensors embedded within the windings, that will be used to turn the power off if the motor overheats. For the very vast majority of the cases, an external unit called an overload relay and set to the motor's nameplate current, will be used to provide this running overload protection.
  • During the starting period for the motor, its inrush and starting current will be much higher than its running current. For this reason, the MCCB or fuses have time/current curves to allow this relatively temporary overload. In some cases, if the motor has a particularly long starting time, additional options would exist, such as selecting overload relays with a longer time delay or even the possibility of manually bypassing the running overload protection during the starting time.

Note, this overload relay is essentially a resistor selected or adjusted to give a calibrated amount of heat output when the motor is running normally. If the current rises for too long, the overload relay will open the thermostat contacts that are embedded within itself, interrupting the control power to the contactor and turning off the motor. Since this is an external simulation of the conditions occurring within the motor, it is approximate at best; corrections must be made if the motor is in a warmer or colder environment than the overload relay, or if the motor has specialized service conditions.

--John M.

Reply Score 1 for Good Answer
Associate
Engineering Fields - Electrical Engineering - New Member

Join Date: Jun 2010
Location: IEC Domain
Posts: 43
#14
In reply to #13

Re: MCCB and MCP

06/09/2010 5:00 AM

Thank You Sir for your valuable output. It was quite helpful and informative.

Regards,

DG EE

__________________
The Crazy Man Talks and The Smart Man Understands
Reply Off Topic (Score 5)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#15
In reply to #14

Re: MCCB and MCP

06/13/2010 7:47 PM

(Just came back from vacation)

Lot of good answers is found in this thread. I would like to add few things about the motor starter:

There are two types of Motor Starter: Non-combination starter and Combination starter.

Non-combination starter = Contactor + Overload

Combination starter = Contactor + Overload + Disconnector + Short Circuit Protection (Fused Switch or Circuit breaker or Motor circuit protector)

The combination starter is again categorized as Fusible combination starter and Non-Fusible combination starter.

Fusible combination starter = Contactor + Overload + Fused disconnect

Non-Fusible combination starter = Contactor + Overload + Circuit breaker or Motor circuit protector (MCP)

Note: The MCP is a circuit breaker with the thermal element removed. It is a brand name of Cutlet-Hammer. It is used in motor starter with thermal overload relay.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Off Topic (Score 4)
Reply to Forum Thread 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bsekhar (1); DamnGud EE (3); ddifferent (1); electricalexpert65 (2); ieshiv (1); jmueller (1); kvsridhar (4); msamad (1); user-deleted-1098 (1)

Previous in Forum: Looking for experienced civil foundation and erection/stringing service   Next in Forum: Dol Starter

Advertisement