Suggestion for Isolation Equipment Selection

06/08/2010 2:51 AM

I have to do modification in 13.8kV, 60Hz system. The scenario is a 13.8kV, 60Hz, 3-core, 240sq-mm, Cu, XLPE cable feeder (length=2.2km) coming from main substaion (protected by SF6 CB and AEG PS451) is feeding an 1MVA transformer (protected by VCB and siemens 7SJ602). Now we are planning construct new residential buildings. For that, we are planning to terminate the cable at new panel (will act as incoming) and taking two outgoings, one for the new building and other for the existing building. The take off point will be at somewhat near to the joint of cable.

Please suggest the new incoming and outgoing isolation types considering proper protection. Will new incoming be just the bus riser panel (no isolation required) or load break switch or CB and the outgoing panel for the existing building that no any panel is required or only isolator will be enough or CB?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Suggestion for Isolation Equipment Selection

06/08/2010 9:37 PM

I would approach the new switchgear for this situation in this way:

Incoming just needs the bus riser - to isolate the whole feeder, open at the upstream main substation breaker. This is often where metering is installed as well.

Outgoing can be manually-operated, fused disconnect switches, with the fuses chosen for protection of the feeder cables to your two (new and existing) buildings, especially if underground. It may take some evaluation to coordinate with the upstream PS451 and your downstream protection. Unless you are going to have significant motor loads at the buildings (you did say they are residential), then a single cable fault won't cause too much heartache from single-phasing if one fuse blows.

Adjust the existing 7SJ602 if needed to (try to) coordinate with the fuse, but its main purpose is to protect the transformer. Someone should do a protective device coordination study on the whole scheme to see how it all fits.

What do you plan for main protection at the new building? Will it be similar to the existing? You will need to try to coordinate it with the upstream fuse, but again, it should protect its transformer first.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Participant

Join Date: Jun 2010
Posts: 3
#2
In reply to #1

Re: Suggestion for Isolation Equipment Selection

06/09/2010 3:23 AM

Thanks alot for the reply.

Yes, the building is residential but it might have some HVAC motorized loads.

The main protection will also be the same as for the existing building.

You suggested that fuse protection will be good enough for the cable feeder of existing building. But if some maintenance activity to be planned out only for the existing, how we isolate the exiting building feeder without any interruption to the new building feeder.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Suggestion for Isolation Equipment Selection

06/09/2010 3:05 PM

That is why each of the two outgoing units is a fused (load-break) disconnect switch. You open the switch for the feeder you want to isolate, and it is de-energized. The fuse provides the protection for the cable, the switch gives isolation / disconnection capability. Simple, reliable, and durable.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Participant

Join Date: Jun 2010
Posts: 3
#4
In reply to #3

Re: Suggestion for Isolation Equipment Selection

06/10/2010 6:49 AM

Thanks alot for your valuable suggestion