Test Procedure of Lightning Arrestor

06/10/2010 6:32 AM

Please give me the test procedure of lightning arrestor.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate
Engineering Fields - Electrical Engineering - New Member

Join Date: Jun 2010
Location: IEC Domain
Posts: 43
#1

Re: subrahmanyam

06/10/2010 7:15 AM

Kindly clarify what you mean by test procedure. Is it testing an already installed Lighting Arrestor?. If so then you would know what it is used for.

Its main function is to create a smooth path for excess over current to the ground.

But i would like to know more the context in which you are asking this question.

Regards,

DG EE

__________________
The Crazy Man Talks and The Smart Man Understands
Register to Reply
Participant

Join Date: Jun 2010
Posts: 3
#3
In reply to #1

Re: subrahmanyam

06/11/2010 3:23 AM

Dear DG EE

We have installed two Lightning arrestors one year back, now i want to test them whether they are working aren't.

Regards,

subrahmanyam

Register to Reply
Anonymous Poster
#2

Re: Test Procedure of Lightning Arrestor

06/10/2010 7:33 AM

Test procedure:- as per international lightning commission ILC 6740

step 1. Create artificial lightning near your arrestor.

Step 2. Check for any damage after the lightning.

This test procedure is not included the lightning protection system, as you asked for only arrestor.

Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: Test Procedure of Lightning Arrestor

06/11/2010 9:48 AM

What is the system voltage at which the arresters are applied? Are they distribution class, intermediate class, or station class?

For arresters applied at medium or high voltage levels, one of the most informative tests is the Doble insulation power factor or dissipation factor (tan-delta) test. It provides values of leakage current (usually in micro-amps) and watts losses that give an indication of insulation quality of the arrester.

That is usually the problem - something compromises the insulation (cracked porcelain, water infiltration, etc.) that causes the arrester to break down and fail other than when it is supposed to dissipate a surge or lightning strike. Newer MOV type arresters, if their insulation is good, can be counted on to handle surges reliably.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5

Re: Test Procedure of Lightning Arrestor

06/11/2010 3:24 PM
__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Register to Reply 5 comments