Air Vent Sizing

06/11/2010 5:26 AM

Dear All,

Water cooling system that operate on pressure 3 bar and temperature 7 - 12 C. We should put an air vent at the highest position on my pipeline, so it can release air that trapped on that pipe.

I have read on an air vent catalog, and i find that selection process for air vent is depend on the required discharge capacity.

is any formula or rule of thumb to calculate discharge capacity?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#1

Re: Air Vent Sizing

06/12/2010 12:35 AM

There is no hard and fast process that I am aware of, but- to be most effective, you should circulate warm water (prior to turning on the chiller) through the system for at least 12 hours after the system is filled and before you start the chiller.

The reason for this action is that the warm water will reject most oft he dissolved air where the chilled water will tend to keep it dissolved and circulating.

I would also suggest that you install the air vent on top of a 12" or longer pipe that is one of the branches of a tee. The tee should be at least 2 pipe sizes larger than the main feeding it. For example- a 4 inch CHW main at the top of the system would discharge into the "branch" of a 6 inch tee with a 12" long x 6"pipe rising from the tee to a vent installed in its cap. The other branch of the tee will be a 6" by 4" reducer an then the 4" branch main should continue to serve the system. This way, the slow water flow will assist in releasing water rather than keeping it moving through the pipes.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#2

Re: Air Vent Sizing

06/12/2010 1:01 AM

During the 1st stage of piping design, the piping isometrics must be furnished with vents and drains at upper and lower points for the purpose of hydrostatic test. And the most common sizes for vents and drains are 1/2" or 3/4". And those vents and drains can be used during the life operation of piping system, and I think that size 1/2" or 3/4" is enough to perform its function.

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply
Active Contributor

Join Date: Apr 2008
Location: International
Posts: 16
#3

Re: Air Vent Sizing

06/12/2010 1:19 AM

Use an air vent device that automatically vent entrapped air using controlled pilot valve operated diaphragm venting valve. These are manufactured accdg to your specs and there's no need for you to calculate the discharge capacity...

__________________
" Almost anything can be reversed through Engineering but not Human Life " WorKerZ