Neutral Earthing for Multiple Transformers

06/13/2010 12:11 AM

Can multiple transformers used with parallel UPS system have common neutral earthing?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Neutral Earthing for Multiple Transformers

06/13/2010 5:01 PM

Yes, I think that the best way for paralleling UPSs insulation transformer including the by-pass transformer is to use a neutral bar where you connect all the neutrals.

Cilmo.

Register to Reply
Active Contributor

Join Date: Jun 2010
Posts: 15
#3
In reply to #1

Re: Neutral Earthing for Multiple Transformers

06/14/2010 12:02 AM

i worried about the neutral currents between the ups and the bypass supply. Also can these neutral currents for a close circulating path between the UPS's.

Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#2

Re: Neutral Earthing for Multiple Transformers

06/13/2010 11:00 PM

Jeesh,, I should hope so!

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Neutral Earthing for Multiple Transformers

06/14/2010 10:18 AM

Each UPS with an Isolation Transformer is a Separately Derived Source and as per NEC (National Electric Code), each sepaartely derived source must be earthed separetly only.