Anonymous Poster

230 V

06/18/2010 8:28 AM

Sir in 230V,1ph AC supply is 230V the RMS value?So what does the volt meter always measures the RMS value?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#1

Re: 230 V

06/18/2010 8:42 AM

yes, electronic ac voltmeters can be designed to read either the average value or the rms value. When you use a voltmeter to measure AC voltage the voltmeter reading shows the rms value of the voltage.

Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#2

Re: 230 V

06/18/2010 9:41 AM

Yes normally we use 230v AC that is RMS value and its maximum value is 230xsqrt2.

Reply
2
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: 230 V

06/18/2010 9:41 AM

The first known man-made source of electricity is a cell, which is DC in nature. But, after realizing the disadvantages of the DC electric equipments, AC Electricity generating machines were invented. When these AC Machines were developed, the power of these machines was to be compared with the already available DC electricity, as it is human tendency to compare anything new with the existing ones. As in the case of steam engines. When steam engines were invented, the power of the steam engines was compared with that of the horses, which were the power sources before the invention of the steam engine. So, a value called RMS Value for AC Electricity was derived which compared the effectiveness of the AC Electricity with that of the DC Electricity. This value is the Effective Value of AC Electricity. As we were more interested in knowing the effect of AC electricity, all measuring instruments were and are designed to measure only the RMS value of AC electricity – may it be Voltage, Current, Power, etc.

Reply Good Answer (Score 2)
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#4

Re: 230 V

06/18/2010 10:18 AM

In AC voltage the current voltage is constantly changing with time. Trying to state a specific voltage at a current point in time would be like stating the time of day to the second - by the time you speak the words, the time has already passed.

Sometimes AC voltage is given as peak value. For a typical 110v system peak voltage is around 170v, which sounds good, but the voltage will only be 170 for a split second at a time, so if you were to hook a 170v device up to it then the device would not operate properly. Plus, peak voltage cannot be used to accurately calculate the amount of work that you can do in a given amount of time (output power), so we use RMS voltage which represents what level the voltage acts like over a period of time if you averaged out the varying voltage level of each individual arc in the AC sine wave.

Here's a link that shows some good illustrations:

http://www.bcae1.com/voltages.htm

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Reply Score 1 for Good Answer
Active Contributor
APIX Pilot Plant Design Project - Member - New Member

Join Date: Jul 2009
Posts: 14
#5

Re: 230 V

06/18/2010 2:07 PM

The RMS is equvivlent DC voltage to the Analogous AC voltage so multimeter(volT)

reads equivalent AC in DC.

Reply Score 1 for Good Answer
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6

Re: 230 V

06/19/2010 12:19 AM

Now that good answers have been given to the original post, it may be interesting to go a little more into "True RMS" measurement...attached is a good article :

http://enginova.com/true_rms_volts.htm

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 2)
Guru
Spain - Member - New Member Engineering Fields - Nuclear Engineering - New Member

Join Date: Oct 2007
Location: Madrid, Spain
Posts: 716
Good Answers: 25
#7

Re: 230 V

06/20/2010 1:08 AM

Hi,

Think on what's AC means... 50Hz, 60Hz.... The only alternative to show the RMS value is to show the instantaneous value (any data acquisition equipment can give it you).

The problem is the response time of the instrument. If you try to see the instantaneous value, it will change from ± peak value frequency times so you Will have not a readable more or less static value. You will see a succession of figures between + peak and - peak. Some multimeters have the "peak" function so you see the RMS value and also the peak value. Ratio between both is RMS = Peak/√2 or Peak times 0.7071.

__________________
It's stupid to discuss about AI: We´ve reached by the "B" way. We' ve producing men as clever as machines.
Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#8

Re: 230 V

06/20/2010 11:00 AM

Some multimeters measure the average positive voltage of a wave form and scale the values using the square root of two readings to produce a display. Also there are true RMS multimeters but they are usually costly to afford. In all it is ok assumed that all multimeters are calibrated to read RMS values.

RMS or Effective values of alternating currents is numerically equal to the direct current that would produce the same amount of heat in a given resistance during one period T of the alternating current as it is actually developed by the latter in that time.

One point we should note is that the DC values are more effective values than their corresponding AC values, meaning the DC current develops a greater amount of heat in the given resistance and time than the alternating current does since the value of the latter remains below that of the direct current, except for the instance when peak values are attained.

One should also be very conscious when taking reading with undefined meters as to know when to apply 0.707 to arrive at the RMS value.

Dickson.

__________________
There is peace in silence and achievement in plans.
Reply Score 1 for Good Answer
Commentator

Join Date: Oct 2009
Posts: 63
#9
In reply to #8

Re: 230 V

06/21/2010 11:24 AM

IN THIS QUESTION, IF IT WERE 230 VOLT 3 PHASE AC SYSTEM IN PLACE OF ONE PHASE?

Reply
Anonymous Poster
#10
In reply to #9

Re: 230 V

06/21/2010 12:11 PM

I'll bite...where can I get a three-phase voltmeter please? With three leads? Four?....

Reply
Reply to Forum Thread 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Dickson (1); EElectrician (1); electricalexpert65 (1); Hameedullah Ekhlas (1); hithuanand (1); kvsridhar (1); Kwetz (1); RAJ089 (1); rwengin (1)