Previous in Forum: Three Phase Variable Frequency Drive   Next in Forum: Third Harmonics Wye-Wye Connection
HV Motor starting
06/24/2010 3:23 PM
1. What is the best starting method for 23MW, 11kV induction motor except electronic soft start.
2. Is ther any advantage if I chang the motor to synchronous one.
3. Will the thyristorised soft starter be more expensive than Korndorfer soft starter? If yes by what percentage?
thanks and regards
Pathfinder Tags: HV Motor Starter
Good Answers: 804
Re: HV Motor starting
06/25/2010 12:54 AM
  1. "Best" is a subjective statement. I think soft starters are best. Others may not agree. You say "except soft start" in your question which implies a bias so I can infer that you do not agree with me, so I can say no more.
  2. Synchronous motors are good when you need slow speeds, and/or you want to run it continuously for the purpose of improving the overall power factor of a plant. If you need high speed and/or PF is not a concern, don't use synchronous, they add complexity. They are also physically larger and the STILL need to be started just the same as an asynchronous motor, so again a soft starter or auto-transformer starter.
  3. At 11kV (which by the way is Medium Voltage, not High Voltage), an RVAT (Korndorfer) starter will probably cost 2/3 the price of a solid state starter up to about 15MW. Above that a soft starter will probably be less and definitely smaller.
06/27/2010 3:23 AM
Appreciated. Thanks a lot.
Looking forward to getting more views from others.
Thanks
Good Answers: 170
06/25/2010 9:26 AM
There is a method called FCMA (Flux Controlled Magnetic Amplifier) Soft Starters. There is a Pune (India) based manufacturer (I think, his name is Innovative Technomics) for these types of soft starters. Try googling "FCMA" or Innovative Technomics.
Good Answers: 804
06/25/2010 4:50 PM
But be aware that there is only ONE source for technical help / design assistance etc. and if you are outside of India, that may be a problem.
07/11/2010 11:10 AM
You are right, Pune based manufacturer is there and I will try to provide the mail Id etc to-morrow.
But it is not known whether they make startes for this capacity discussed in this thread.
sdr710
06/26/2010 9:47 AM
First of all at this rating it is necessary to know what is the load .If it is a high inertia drive like a fan or low inertia drive like a pump, speed etc before a satisfactory answer can be suggested.Also 23 MW starting means you should have a strong system.what is the main transformer capacity and also the capacity of the transformer supplying this motor.Further new series of motors with low starting current of3.5to 4 times rated current as achieved with a soft starters are available.For this type of rating one has to carefully chose the motor. Synchronous motors are useful where very low speeds are involved and where PF can be maintained at a higher value by controlling the excitation.