15 kVa Transformer Hookup?

06/24/2010 9:47 PM

I hooked up in my factory a 15kVa 600/240 1ph addition transformer feed from a transfer switch and 2 different switch rooms. The transformer feeds a 4kVa UPS. The input for the UPS is 240V , no neutral. The secondary of the UPS produces a 1ph 120/240V system which feeds the control room in Power House #1.

I have run #2 ground as required and bonded the UPS/TRANSFORMER/Transfer switch to the ground bus that runs around the switch room where it is all located it in minus the LP for the control room.

The transformer needs a jumper between the 2 secondary windings to produce the 240VL-L output. He stated that this "neutral" needs to be grounded to the ground bus with #2 as well. I don't see a point as there are fused points on the high side of the transfer switch, along with fused point on the upside of the UPS and a main breaker in the LP.

The UPS "creates" a neutral on the secondary side of the UPS...... So why do I need to ground and thus create a neutral in the transformer if it doesn't really go anywhere?

Thanks for any help.

Cheers

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#1

Re: 15 kVa Transformer Hookup?

06/25/2010 6:51 AM

If the transformer is not grounded; in the event of earthfault on any of the transformer phase connectors, the healty phase voltage if you happen to measure it shoots up: objectionable isn't it.

It seem you have grossly misinterpreted the earthing requirements given by the vendors; Transformer neutral is to be first connected with an earthing rod/pit and than carry out bonding with transfer switch and metal enclosuere of the UPS, while the internal earth of UPS at the output sourcing (electonic card earth) should have a distinly seperate earth system.

Connecting the out sourcing of UPS to the electrical erthing bus will provide considerable distortion to the 4-20 milliamp instrument fuction as well as DCS (if has been installed) to frequently disrupt the proper functioning of the Control Room.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply Score 1 for Good Answer
Anonymous Poster
#2
In reply to #1

Re: 15 kVa Transformer Hookup?

06/26/2010 12:09 PM

The transformer, transfer switch are independantly grounded to the ground bus va #2 . The system is all bounded together with the #6 in the TECK Cable. And there is an ind. ground wire, #2 from the neutral-ground jumper on the secondary of the UPS to ground.

It has been installed according to manufacture specs and my own common sense.

Just was not sure why I needed to ground the jumper on the tranny.

Thank you for your info, I will check it out.