Restricted Earth Fault Relay
06/25/2010 9:08 AM
Where does this "restricted" adjective comes from? Thank you...
jinxnao
Good Answers: 170
Re: Restricted earth fault relay
06/25/2010 9:14 AM
It is because that this particular protection scheme/relay would operate only (and only) if the earth fault happens within a pre-defined zone. If the earth fault happens out side this pre-defined zone, this relay would not respond, even if the fault current is beyond the setting made in this relay. For such "external" faults, other "non-restricted" or conventional earth fault relays would operate.
As the operation of this relay depends upon the fault occuring within a "restricted" zone, the adjective "restricted" is used.