short calculation with solved example

06/25/2010 9:56 AM

how i can calculate the short circuit current if my MDB Main breaker is 1600A AND transformer is 1000KVA AND lenght is 72m

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: short calculation with solved example

06/25/2010 10:07 AM

Check here. This is a straight forward example.

http://ecmweb.com/mag/electric_shortcircuit_calculation_methods/?smte=wr

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: short calculation with solved example

06/25/2010 10:20 AM

Assuming that the transformer secondary is 433V and the percentage impedance of the transformer is 4%, the short circuit current for a three-phase fault would be:

(1000 x 1000) / (Root 3 x 433 x 0.04) = 33,335A or 33.33kA.

Note: It is assumed that the 72m is the length of the bus dust whose impedance is neglected in the above calculation. If the bus bar impedance has to be included or if the 72 m shown is that of a cable from the transformer to the panel, then the cable impedance has to be considered and the fault current will reduce considerably. But, the above value can be taken as a safe design.

Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#3

Re: short calculation with solved example

06/25/2010 10:21 AM

For short circuit rating you have to take into account %age impidence of the transformer, rated voltage is to be known as well.

Length of cable or bus duct provides additional limiting impidence however motors contribue and if the motors are of large size there will be considerable effect.

Without going into detailed calculations 30 KA short circuit rating at 400 volts works well with 1000 KVA and is widely practiced.

Symmetrical short circuit current formula with only the transformer under consideration is as follows:

Symmetrical Short Circuit KA = In x 100/%Zt

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#4

Re: short calculation with solved example

06/25/2010 12:29 PM

See this pdf and it will help you step by step.

http://www.bussmann.com/library/docs/EPR_Booklet.pdf

Reply Score 1 for Good Answer
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); Hameedullah Ekhlas (1); mountk2 (1); wareagle (1)

Previous in Forum: transformer   Next in Forum: help me

Advertisement