Transformer Impedence

07/02/2010 4:38 AM

Presently we are proceeding through power generation expansion plan.addition of new equipment is leading to fault levels beyond acceptable levels.As generator step up transformer ,I desire to have 10MVA transformer 33/11KV with percentage impedance of 12% as part the effort to reduce the fault level on the existing 33KV bus bar which its limited in short circuit rating.Our existing 33KV transformers have 8% impedence.Is it possible to achieve the desired specifications.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#1

Re: Transformer Impedence

07/02/2010 1:26 PM

Theoretically yes but practically it would be asking too much from a manufacturer to prvide something non-conventional, I would say rather stick to the transformer manufacturer's norms.

To reduce short circuit level try one of the following:

(a) Intertripping arrangement for feeder circuit breakers.

(b) Changing of overcurrent relays from Time grading to combined Current grading.

(c) Use of current limiting series reactors.

(d) Currently available CB's are of very high interrupting capacity consider minor alteration of your switchgear setup.

(e)Consider microprocessor based monitoring systems, some manufacturers such as ABB have commercialized these.

(f) change of BTD to cables etc.

Take into account that generators have high value of synchronous reactance, I mean don't get carried away by jargon, do your home work to assess if there is a real problem and if it is so what is the intensity of it.

When the problem is well defined chances are you will have simpler and more practical solutions in hand.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2
In reply to #1

Re: Transformer Impedence

07/02/2010 1:35 PM

Asking a transformer Mfr to provide 12%z instead of 8%z is not so unconventional. The utility that employs me does it all the time in certain of its territories where stations are very close, load is concentrated, and fault currents are very high. They purchase power transformers from various vendors up to about 13%. It does work.

In my territory, your item (c) is also very common.

I think the OP's concern is not to have to replace other equipment that might be overdutied by the addition of this new unit. However, he would have to do an analysis of what each option would cost (replace a bunch of breakers, additional bus bracing, etc.)

A good short circuit & system study should show where the problem spots are, and then the alternatives could be evaluated.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Participant

Join Date: Jul 2010
Posts: 2
#3
In reply to #2

Re: Transformer Impedence

07/03/2010 5:34 AM

Thanks for the comments.Can u Please let me know the manufacturer who has supplied the transformers with higher than normal %age impedance.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4
In reply to #3

Re: Transformer Impedence

07/04/2010 8:55 PM

Waukesha Electric has done it for us. Also Pauwels and I believe ABB.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply