How Many 2 ton Window A/C Runs on a 125 KVA Generator ?

07/12/2010 4:41 AM

How many 2 ton window A/c can runs on a 125 KVA generator ?

Register to Reply
This discussion was "closed" on 07/13/2010 7:31 AM. No new comments are allowed.
Message from admins:
This is a duplicate posting. Please respond in the other thread: http://cr4.globalspec.com/thread/56664
Anonymous Poster
#1

Re: How many 2 ton window A/c can runs on a 125 KVA generator ?

07/12/2010 6:33 AM

Sir,

125 Kva set is expected to take 100 Kw @ 0.8 pf.

The electrical load of 2 T window AC will be 3 Kw. You can connect 13 units per

phase ie 39 units in all. But you have to use timer and contactor controls (for

delayed starting ) so that the load will not be sudden. The starting current of 2 T

unit @ 220 volt will be around 25 A for 5 seconds. The starting system should

ensure that even the stabilisers ( 5 Kva ) are switched on in a phased manner.

With Due Regards,

Manroop.Chennai.

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: How many 2 ton window A/c can runs on a 125 KVA generator ?

07/12/2010 8:00 AM

Mr can you explain me how 13 units per phase calculation is done?

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: How many 2 ton window A/c can runs on a 125 KVA generator ?

07/12/2010 9:17 AM

I think he already did, re-read the post above.

Register to Reply
Register to Reply 3 comments
This discussion was "closed" on 07/13/2010 7:31 AM. No new comments are allowed.
Message from admins:
This is a duplicate posting. Please respond in the other thread: http://cr4.globalspec.com/thread/56664

Previous in Forum: If the Ceiling Fan is on Slow Speed, Does it Consume Less Electricity?   Next in Forum: Phases
You might be interested in: KVA Meters, Window, Glass and Glazing Services

Advertisement