Anonymous Poster

Small 3-Phase Genset Loadbank Testing

07/13/2010 11:41 PM

I'm trying to sort out loadbank testing for 3-phase 16kW/20kVA genset. The genset runs 24 hours a day but only under load around 10 hours a day at no more than 30% load. Genset powers 3 x VFD to remote located pumps. Our Northern brothers connect their loadbank for up to 24 hours with around 15% load. I have previously been involved with running Cat gensets for standby power in offices and highrise building where we ran them up to 110% load for a short period. So...

should I follow the standby practive and slowly (over say 4 hours) ramp the genset up with up to 1 hour at 100 - 110% load, or follow the other path of low load for extended period? what are the pro's and con's?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#1

Re: small 3-phase genset loadbank testing

07/14/2010 12:17 AM

The manufacturers recommend a minimum of 30% (or atlest 25%) load to run the genset, failing to fulfill this requtrement; initialy the exhaust gas colour changes from light grey to dark smoke, in the long term dammage to primemover can occour.

Thre is not much sence in runing the generator to 100-110% load on a regular basis it can be left for special occasions.

Check out manufacturers recommendations for generator loading and comply with the instructions.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Anonymous Poster
#2

Re: Small 3-Phase Genset Loadbank Testing

07/15/2010 2:20 AM

During low load condition, you may provide the old concept of running the unit with a load test bank by installing/fabricating the following:

1. Fabticate load test bank made of steel plate or other materials and install insulator

2. Install bus bar with wench (manually operated) to control the loading of genset

3. Mixed salt and water (approx. 1/2 sack of salt for every 5cu.m of water) - excessive boiling indicate to much sal content.

4. Install temperature sensor if required

Please insure that safety will be considered in doing this task .

Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#3

Re: Small 3-Phase Genset Loadbank Testing

07/15/2010 4:29 AM

You could also use an electrical heating as load for your gen set. Mostly they have a power around 3 or 4 kW and they are not expensive. Buy 3 or 4 pieces and connect them equally distributed on your gen set.

Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#4

Re: Small 3-Phase Genset Loadbank Testing

07/17/2010 4:26 PM

Am interested in this question but ur not specific to what U want. Let me get ur point.

Dickson

__________________
There is peace in silence and achievement in plans.
Reply
Anonymous Poster
#5
In reply to #4

Re: Small 3-Phase Genset Loadbank Testing

07/28/2010 6:19 PM

Ok, so I have contacted the supplier/manufacturer who advise to apply an initial load of 30 to 50%, run for around 1hour. Then apply load around 75% and run for another hour. Finally, apply load at 100% and run for another hour, and then reduce the load following the same pattern as it was applied. I am led to believe the main purpose is to have the diesel engine clear contaminants/unburnt fuel. However, if there is significant glazing it may take more time to clear from the engine.

This genset runs 24hours a day and feeds 3 motors running pumps. The system monitors water levels - set point of say 50m, when water reaches 55m pumps start until the water drops to 45m when pumps stop. The pumps vary in run time from running every hour to running once a day. Loading works out around 15% for each pump so that the genset never runs more than 50%.

My cautious side says to not run the genset under full load for more than a few hours at most. The diesel fitter wants to run the genset under full load for up to 24hours. The supplier/manufacturer recommends not more than 2hours.

Extra question/s - what is the likelihood of damage to the alternator if running at or above 100% load for more than a few hours? what sort of damage may occur? If glazing has occured what sort of time at full load may remedy/reduce the situation?

Reply