VFD power factor at reduced loads

07/14/2010 2:20 PM

Hello,

I have a question about the deterioration of the power factor of a VFD operating under reduced loads. Typically, the input current on each line of a 3-phase VFD will exhibit peaks corresponding to when the input voltage is above DC bus voltage. Under reduced load (i.e. lower VFD output current) these peaks will be sharper due to the fact that the DC bus loses less charge and the input voltage is higher for a shorter period of time.

Does anyone have any quantifiable data/graphs/waveforms to illustrate the extent to which this happens on a typical VFD and, more critically, how reduced power affects the distortion power factor?

Thank you in advance for your help,

Pawel

Register to Reply
Pathfinder Tags: VFD "power factor"
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#1

Re: VFD power factor at reduced loads

07/15/2010 10:51 AM

I do not like the I thd or PF measurements done by most power meters.

The I thd will likely increase as the current is reduce and become useless at low current. While the amount of real harmonics current is reduced, the RMS current may be reduced faster and their ratio (I thd) increases. This gives a false interpretation and often forces manufacturers to install harmonics filters that are not necessarily needed.

The Power factor also becomes meaningless at low current as the KVARs generated and the real power are both low. Their ratio can look very bad but it has no effect on the plant because very little KVARs are actually generated.

What is important is not how bad a load looks but what is its effect on the plant feeder. That depends on its size with respect to the feeder.

I hope that this will clear some of the confusion.

Regards

Marco

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.