parallel piping system

07/15/2010 4:42 AM

i just want to know if in electrical circuit, the equivalent resistance of a parallel circuit is given by 1/Rp=1/(1/r1+1/r2+........1/rn). Then is this relation true for parallel piping also for finding equivalent pressure loss in a parallel piping system? since the parallel piping and parallel electrical circuit is similar.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Feb 2007
Location: Aberdeen, Scotland
Posts: 393
Good Answers: 21
#1

Re: parallel piping system

07/15/2010 5:37 AM

I'm not an electrical engineer but I think your equation is wrong. It should be

1/Rp=(1/R1+1/R2+......1/Rn)

To be honest I'm not sure if running parallel pipes follows this relationship. Thinking out loud, if I have a header tank with one pipe coming out the bottom and have X flow then I put in another identical pipe I'd get 2X flow. This would mean that the resistance would have halved if the relationship between flow and resistance is linear. Now I seem to remember that it is not so I'd suggest the relationship isn't as simple as the above equation suggests.

Thats my thinking of it. Can someone prove (or disprove) this with calcs?

Register to Reply
Participant

Join Date: Jul 2010
Posts: 3
#2
In reply to #1

Re: parallel piping system

07/15/2010 5:59 AM

thank u for your comment. yes i was wrong earlier. i maen to say 1/Rp= (1/R1+1/R2+...1/Rn). while designing a parallel piping system with different flow rate in different branch, how would i calculate the pressure differnce. should i use this formula to calculate equivalent pressure loss?

Register to Reply
Member

Join Date: Jun 2010
Location: surabaya, Indonesia
Posts: 9
#4
In reply to #2

Re: parallel piping system

07/15/2010 7:59 AM

No, you can not do like that.

Every pipe branch point have the same pressure.pressure drop in a branch is same as much in another pipe.

if A is the branch point which divided into 2 branch, and B is the branch point that 2 branch mentioned can become unity again. The pressure drop is pd A minus pd B, this value will be equal with Pressure Drop on every branch.

Register to Reply
Anonymous Poster
#3

Re: parallel piping system

07/15/2010 7:47 AM

Yes, basic principals apply to both systems.

The sum of the flow at a node is zero. Current is analogous to flow. KCL.

The voltage around a loop is zero. KVL.

Replace V=IR with Q=VA and you are good to go.

Use Bernoulli equation to balance potential and kinetic energy plus friction losses.

Did your circuit also contain reactive components (i.e. capacitance and inductance)? You did not say.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5
In reply to #3

Re: parallel piping system

07/16/2010 9:22 AM

It's not that simple. In elec case, voltage difference is proportional to current, but for fluid flow pressure difference is proportional flow2 in nearly all practical cases. Also V=IR is Ohm's law, but Q=VA is just velocity x area and doesn't say anything about pressure difference.

But there is a formula analogous to 1/Rp = 1/R1+1/R2+......1/Rn

Calling R1 = ΔP/q12, R2 = ΔP/q22, etc (analogous to R1 = V/I1, R2 = V/I2), q1 = √(ΔP/R1), q2 = √(ΔP/R2) etc. To calculate R1, R2 etc, just take an arbitrary (but reasonable) figure for q, find ΔP by usual hydraulic methods, and find ΔP/q2. Doesn't have to be the common ΔP for the overall system.

qtot = √(ΔP/Rp) = q1 + q2 + ...... + qn = √(ΔP/R1) + √(ΔP/R2) + ....... + √(ΔP/Rn)

So, dividing by √ΔP, 1/√Rp = 1/√R1 + 1/√R2 + ....... + 1/√Rn

Cheers......Codey

__________________
Give masochists a fair crack of the whip
Register to Reply
Participant

Join Date: Jul 2010
Posts: 3
#6
In reply to #5

Re: parallel piping system

07/17/2010 6:04 AM

thanks codey 4 your answer. but i am little confused about the relation Q1=√(ΔP/R1) since the unit of ΔP & R1 are same and is expressed in ft of water in case of a hydronic system designing. please clarify it.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7
In reply to #6

Re: parallel piping system

07/17/2010 7:30 AM

Hello khurshid

No, R has units ΔP/Q2. So ΔP/R has units Q2.

E.g. to take arbitrary figures, if ΔP = 10000 Pa at flow 100 m3/h, R = 1000/1002 = 0.1 Pa/(m3/h)2.

Come back if you need more.......Codey

__________________
Give masochists a fair crack of the whip
Register to Reply
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#8

Re: parallel piping system

07/17/2010 10:05 AM

I have many times tried to use electrical/hydraulic analogies looking at circuits of each. For the most part they are equivalent.

However, if you want to stretch you mind, examine the units of your electrical or mechanical equations. It is then you may decide on personal limits of inquisitiveness.

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Register to Reply
Register to Reply 8 comments