Relay Contact Rating

07/16/2010 9:11 AM

What is the formula that dictates the current rating of the relay contacts. For example, how much curent the relay contacts can handle at 120VAC if the relay contact is rated for 250VAC and 10A contact rating. I was told by some supplier that the relay can handle more current at 120VAC but I want to know what electrical formula drives for the relationship to make sure the statement is true. I would appreciate if some one can answer that.

regards

__________________
The success is determined not so much by the size of one’s brain as it is by the size of one’s thinking.
Register to Reply
Pathfinder Tags: Relay contact rating
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
6
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Relay Contact Rating

07/16/2010 9:56 AM

There is no single simple formula to relay contact ratings. The effectiveness of different contact area, materials of the contact, oxide layer depth, contact motion all play a part in the non-linear transitions of making and breaking contact. But your vendor is pulling your leg to say that a relay rated to handle 10A @ 250VAC can now reliably handle say 15A @ 120VAC. Most manufacturers consider the contact rating number the corner of a region that their component is rated to handle continuously. Exceed 10A (continuously) at any voltage and it might work for some reasonable amount of time. But don't blame the manufacturer whenever it fails or ignites, they warranted only 10A should flow through the contacts.

Ask the vendor if they would be willing to put in writing that their company will assume liability for the relay's use outside of the manufacturer's ratings. Notice the response you get to that request.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 6)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Relay Contact Rating

07/16/2010 11:35 AM

Redfred said it all! GA.

'Relay' in the IEC countries can mean any one of (a) Contactor relay, which is a small contactor, (b) Protective relay, like overcurrent, earth-fault, ... any protective device which will have an output 'relay', smaller than (a) above, (c) the small snap-action switch in a thermal overload relay .... actually 'relay' is quite a vague name

A standalone small contactor will have a much higher rating than the snap switch of a thermal relay by construction alone. Then there is the Pandora's box of DC ratings, which often require relays to have permanent magnet blowouts....

Anyway, there is no formula .. you need to test for every rating you want to assign (sigh)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 134
Good Answers: 11
#3
In reply to #2

Re: Relay Contact Rating

07/16/2010 12:26 PM

Read the manufacture's data sheet for the relay.

Yes I would expect the relay to be able to open more current at 120 volt than 240 volt.

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#5
In reply to #2

Re: Relay Contact Rating

07/16/2010 12:53 PM

I like the "AC-X" ratings the IEC uses for the type of load, very convenient.

__________________
CRTL-Z
Register to Reply
Participant

Join Date: Jul 2010
Location: Griffin, Georgia
Posts: 3
#4

Re: Relay Contact Rating

07/16/2010 12:28 PM

Here is another point of view that I want to share with you guys. This came from one of our very senior engineer that I really respect.

"The contact rating depends on the wattage. So at 250VAC and 10Amp rating, the wattage would be 2500 Watts. So for 120VAC you divide the same wattage 2500 by 120 and you will get 20.83 Amps." So it will pretty much double the current rating of the contact at 120VAC.

Any thoughts!

__________________
The success is determined not so much by the size of one’s brain as it is by the size of one’s thinking.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #4

Re: Relay Contact Rating

07/16/2010 12:58 PM

With respect, it is true but only within some limits. Just think, would the relay be able to handle 100A at 24V AC? Not likely isn't it ? So there are many ratings of the relay contacts per se....

Carrying capacity, Making capacity and Breaking capacity. And, while it may be able to make and break double the current at half the voltage, it may not be able to carry it !

So you need to follow the manufacturer's recommendations.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7
In reply to #4

Re: Relay Contact Rating

07/16/2010 1:20 PM

Now we're into a completely different set of realms. First, there's the obvious engineering aspects of relay contacts. Second, there's the corporate pecking order between you, 6Sigma, and your respected senior engineer.

To the first point you will notice that this relay on page 3 specifies a contact rating of 10A @ 250VAC and 15A @ 125VAC. What is rare to find for many relays is that on page 4 there is an actual chart showing the various maximum approved currents for AC and DC voltages. Now I doubt that you happen to be using this particular relay. So your engineer maybe correct for the relay that has been chosen.

To the second point, it is the senior engineer's responsibility to oversee and approve all (appropriate) engineering criteria. If he/she is certain that this relay can handle the higher current, that is his/her call. (English really needs some gender neutral pronouns.) So tread carefully in questioning this conclusion. A safe method for you will be to obtain a print out of the manufacturer's data-sheet for your relay and the relay data-sheet I directed you to. At an appropriate time ask this engineer to educate you on how the relay you are using meets the higher current rating. You may find that this may just be a misunderstanding between the two of you in the actual circuit being controlled, which ratings you are concerned with, or a variety of other plausible scenarios. But do not push this to hard. You already have an authorized opinion.

Good Luck

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Participant

Join Date: Jul 2010
Location: Griffin, Georgia
Posts: 3
#8
In reply to #7

Re: Relay Contact Rating

07/16/2010 3:22 PM

Thanks redfred for valuable input. Thanks all .

regards

__________________
The success is determined not so much by the size of one’s brain as it is by the size of one’s thinking.
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#10
In reply to #7

Re: Relay Contact Rating

07/16/2010 10:51 PM

This reply is FIRST relative to gender neutral pronouns in English- the word "their".

SECOND- Relative to how much POWER (in amps) a contactor/relay can handle not only depends on the ability of the metallurgy to support the amount of energy moving through it without fusing together (welding itself shut)- there is also the ability of the contactor/relay to OPEN the circuit. As voltages increase, the potential for continued power transfer to occur as the device opens greatly increases.

Based on that issue, it IS reasonable that a relay rated for 10 amps at 240 VAC MIGHT be able to break a circuit drawing 15 amps at 120 VAC and its metallurgy could very well be able to handle that power flow. That said, unless I see it stated in the manufacturer's catalog or data/spec sheets, there is NO WAY I am going to put more amperage through any contactor/relay that is not rated for that load.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#9
In reply to #4

Re: Relay Contact Rating

07/16/2010 6:42 PM

6Sigma writes :"This came from one of our very senior engineer that I really respect.

"The contact rating depends on the wattage. So at 250VAC and 10Amp rating, the wattage would be 2500 Watts. So for 120VAC you divide the same wattage 2500 by 120 and you will get 20.83 Amps." So it will pretty much double the current rating of the contact at 120VAC."

I would ask this 'very senior engineer' which manufacturers make such contactors?

The GE contactors, for instance, are all limited by current, not power. As a specific example of a bread-and-butter contactor, the CL02-series will switch 12KW at 220V, 27,5KW at 500V, Ith = 18A max. AFAIK, the other major manufacturers (Schneider, Siemens, Moller, ABB,...) all follow the same prescription.

I know from experience analysing fried contactors that if you attempt to switch even a gnat's whisker more current than the rating, the contactor will have a depressingly short life, the contacts will overheat due to I2R heating. If, as per 6Sigma's scenario above, you attempted to switch a 12KW load at 120V with a CL02, you would need to be quick in closing the switchboard door to avoid seeing it melt before your eyes.

__________________
paulusgnome
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#11
In reply to #4

Re: Relay Contact Rating

07/17/2010 3:10 AM

Lets look at that from a slightly different angle.

Say you have a cable working at 1000V @ 1amp = 1Kw

and you have a cable working at 1000amp @ 1v = 1Kw

Do you suppose the cables would be the same size? I think not.

As others have said only within strict parameters, and as noted at lower voltages the current rating does not double also the voltage ratings are not directly interchangeable from a safety point of view as well as a construction requirement.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#12

Re: Relay Contact Rating

07/17/2010 12:09 PM

At the other end of the scale, is the minimum current, with it's own set of problems.

__________________
CRTL-Z
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#13

Re: Relay Contact Rating

07/19/2010 1:32 AM

Dear CR4s,

Mathematically 10 x 250 = 20 x 125 , Fine. The relay contact are designed to carry say 10 A safely (with the given area of contact through which the 10 A flows ) Any mathematical jugglery will harm the relay by over loading the Contact

points ( Current density will double - contact heat dissipation will be a problem) Donot ask me whether 5A x 500 v will be safer !!

Manroop.Chennai

Register to Reply
Anonymous Poster
#14
In reply to #13

Re: Relay Contact Rating

07/19/2010 7:46 AM

Hi Manroop,

I believe that it will be a problem. Heavy arking will take place at the time of switching. If you want to use the relay for that kind of application, you may use a triac in parallel with the contacts. Make sure that the triac's blocking voltage is not less than 800V when you are switching 500 VAC. The triac gate current must be maintained at least 50 ms after the power to the relay coil is removed. This way you can equalize the electrical life to the relay's mechanical life which at least ten times its full load life. A well designed relay can be used to carry up to ten times its rated current at highest rated voltage if protected by a triac.

If you are switching DC use a power MOSFET as protection devise.

Job Thykkoottathil

Register to Reply
Register to Reply 14 comments