DP Level Transmitter Questions

07/21/2010 1:05 PM

I am just starting out in Instrumentation and was looking at a DP level transmitter today that is monitoring the water level in the bottom of a flare. The transmitter measures off a bridle that has about 8 inches in between the HP and LP taps. My question is: why do we have to fill both impulse tubing lines with water (or gylcol)?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
5
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#1

Re: DP Level Transmitter Questions

07/21/2010 3:25 PM

Usually, the pressure transmitter tap on the lower elevation side is not 'filled' with fluid, rather the process fills that line through gravity: liquid flows downhill. That's how the head pressure of column of liquid is transmitted to the pressure transmitter.

The upper elevation tap is called the reference leg.

The key performance criterion for a reference leg is that the reference leg provide (or represent) a constant, known, hydrostatic head; it's the reference point.

When filled with a liquid to provide a constant reference leg pressure, it's because

- the tank is pressurized and the measurement has to be a differential measurement, not a gauge pressure measurement referencing the atmosphere

- the liquid in the tank is likely to condense and collect in the impulse tube which will directly affect the accuracy of the reading. With condensate in the impulse line, the condensate will apply not just a blanket pressure to that leg, but blanket pressure plus the condensate's head pressure.

So to avoid varying amounts of condensate head pressure and its associated error in the reference leg, the reference leg is filled to start with, and is left filled and the fill fluid constitutes a known hydrostatic head reference point.

Reply Good Answer (Score 5)
Associate
Pakistan - Member - New Member

Join Date: Dec 2009
Posts: 29
#2

Re: DP Level Transmitter Questions

07/21/2010 3:35 PM

Dear,

Do you know about Wet and Dry Calibration.

You can use Dry LP Leg Calibration of DP Tx. when your LP tap are on the top of Tank or Vessel Because liquid can not entrained gas or air.

But When you see that the LP tap is at the side of the tank you cannot use Dry LP Leg Calibration because due to over filling. In this problem you should use Wet LP Leg Calibration by filling Water or any other process Fluid.

I can send you Auto Cad Drawings.

CR4 Admin - Personal information removed

From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses.

__________________
AUR
Reply Off Topic (Score 5)
Member

Join Date: Jun 2010
Posts: 8
Good Answers: 2
#3

Re: DP Level Transmitter Questions

07/22/2010 2:57 AM

Another reason the lines, plus sometimes "pots" are filled with glycol is to protect the bellows or sensing portions of the measuring instrument from the damaging effects of the process being measured. Whether it is corrosive, temperature, etc.

An example would be steam, the glycol is used to sort of isolate the measuring device from the obvious temperatures of steam.

Reply Score 1 for Good Answer
Commentator

Join Date: Jul 2010
Posts: 75
#4

Re: DP Level Transmitter Questions

07/27/2010 8:02 PM

by the way, just a matter of clarification to be exact.....in an open tank application wherein one side of the dp (lo pressure side), most likely vented to atmosphere, is it required to have it filled the lo presure side impulse pipe with water to serve as reference leg?

thanks and much appreciated

Reply
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#5
In reply to #4

Re: DP Level Transmitter Questions

07/28/2010 12:01 AM

Hi,

When measuring level in an open tank using a D/P cell is not necessary to have impulse tubing or pipe on the low side, neither is necessary to have it filled with water.

Venting the low side to atmosphere at the D/P cell is sufficient.I think there is some posts where there is an explanation about this, if you can't find them I will explain it to you.

Thank you

__________________
"The older I get -The better I was"
Reply
Commentator

Join Date: Jul 2010
Posts: 75
#6
In reply to #5

Re: DP Level Transmitter Questions

07/28/2010 1:06 AM

thanks for immediate reply. but i think, i need the explanation since i find it hard to locate the post.

much appreciated

Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adeebulrehman (1); Carl_E (1); valski (2); wailinharp (1); wrenchpuller (1)