Relay Range

07/25/2010 9:37 AM

i want to use 100/5 ratio ct coil as overload relay on 70 amp load.what amp range relay & setting required for this application ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: relay range

07/25/2010 9:45 AM

At 70A primary you will get 3.5A in the CT secondary. You can use a relay which has this current setting near its top rating, so that it cannot be set too high by mistake. You need to also see that the CT is capable of delivering this current through the relay...in other words the relay burden of the CT should be adequate.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Good Answer (Score 2)