Hipot Testing on Cables

07/25/2010 10:19 PM

There seems to be no commonly acceptable standard/or practice on the test voltage and the duration for the hipot tests on the HV cables.

For example,for a 33KV cable commissioning test after laying,DC voltage of 67KV dc (twice the system voltage + 1 kv) for 15 mts.is in vogue in INDIA.

Engineers now opine that this is not safe for the cable,1 mt. or 5 mts duration is ideal.

Better still is to test the cable with a VLF (very low frequency such as 0.1 H etc) at a

much lower volt and shorter duration than DC hipot test.

Specialists' recommendation with proof of authority when in dispute will be very helpful

to the community.

Register to Reply
Pathfinder Tags: high volt testing hipot tests
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Hipot Testing on Cables

07/26/2010 12:15 PM
Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2010
Location: UK
Posts: 89
Good Answers: 2
#2

Re: Hipot Testing on Cables

07/27/2010 1:12 AM

there was a discussion earlier this year on this subject and I can't find it, however, there are white papers that say consistent high voltage testing of cable does more harm than good and causes micro-cracks in the insulation.. again I wish I could find that paper

I've included a few links that might be helpful

http://www.cirris.com/testing/guidelines/hipot_testing.html

This pdf is VERY enlightening

http://www.imcorptech.com/Papers/Utility%20Experiment%20Verifies%20Destructive%20Nature%20of%20VLF%20HIPOT%20Withstand%20Testing.pdf

and finally

http://www.emersonprocess.com/Home/library/articles/maintfacts/maintenancefacts0310_hipot-testing.pdf