Anonymous Poster

DG set selection

07/31/2010 9:36 AM

Dear sir;

We have a construction going on. It is a hostel with 16 rooms. Every room will have 1 tubelight and a fan. Apart from this we will have around 20 lights around the building for public utility space. The hostel has a solar assisted electric water heater + one borewell to lift water for 5 floors. Could you please recommend the correct DG that we need to buy. Jsut behind the hostel we have residential area. Thanks in advance.

Rgds,

Prashant

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#1

Re: DG set selection

07/31/2010 9:50 AM

As you mention a motor load (pump) I would suggest contacting the manufacturers of gen sets with your load data and sound emission concerns. The motor starting capabilities and other characteristics of generators vary widely between manufactures.

__________________
CRTL-Z
Reply
Anonymous Poster
#3
In reply to #1

Re: DG set selection

07/31/2010 9:05 PM

Why not you intellectual giants give some tips to reach a solution for the problem asked by someone. Some fresh engineers just need a support to execute. Else please dont take that risk to answer.

Reply Score 2 for Off Topic
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#8
In reply to #3

Re: DG set selection

08/01/2010 9:08 AM

Please accept my apology, I was trying to point out that motor loads (in this case, an unknown) require that the generator be able to supply the additional inrush current required for starting these motors. Some generators of a given output rating are capable of this, others are not. The generator manufacturers can provide information regarding this. This was a "Tip" to reach a solution.

__________________
CRTL-Z
Reply
2
Anonymous Poster
#2

Re: DG set selection

07/31/2010 10:20 AM

hire an engineer to do this job for you.

Reply Good Answer (Score 2)
Anonymous Poster
#4
In reply to #2

Re: DG set selection

08/01/2010 1:46 AM

that's right what you have to do contact some company like Siemens Engineering they will come to your hostel and check out the possibilites an reqiurement of your hostel and then wil suggest you the Genset. I hope you got it

Reply Off Topic (Score 5)
Associate

Join Date: Jun 2010
Posts: 34
#5

Re: DG set selection

08/01/2010 2:24 AM

Load calculations are:

1- 16 rooms with one twin tube light fittings of 40 watt each.

2- 16 ceiling fans of 100 watt each.

3- 20 lights of 100 watt each for the general area.

4- water heater 5000 watt.

5- Pump motor 10 kw.

16x2x40 = 1280 watt

16x100 = 1600 watt

20x100 = 2000 watt

water heater= 5000 watt

pump motor = 10, 000 watt

total load = 19,880 watts.

125% of 19880 watts = 24,850 watts

Add 25% for future extension.3106 watt

A genset of 30 kw shall be enoug. you can adjust the loads on the real values.

if your tube lights are using megnatic ballasts then multiply the wattage of the tube with 1.8 to calculate its load.

you can adjust the load of the pump on real basis and reduce the solar assisted water heate load and apply the selection method given above.

you can enquire from the market and now a days you can get acoustic generator set very easily with a sound level nearly equal to a car engine.

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6
In reply to #5

Re: DG set selection

08/01/2010 8:36 AM

You should consider the diversity factor,otherwise you will recommend over-sized genset which is not economical.

__________________
pnaban
Reply
Associate

Join Date: Jun 2010
Posts: 34
#7
In reply to #6

Re: DG set selection

08/01/2010 8:48 AM

1- What diversity factor would you consider in a boys hostel, where quantity of every equipment is just one .

2- Mind it that it is a boys hostel, so who cares policy will prevail, everything shall be working even when they are out for class etc etc.

3- the guy did not mention small power points (sockets) + the service areas like kitchen etc, so these were also taken into account.

4- If the supply is 100% dependent on generator, I will suggest two, one working one standby.

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#9
In reply to #7

Re: DG set selection

08/01/2010 9:19 AM

The best way to do things is to follow some recognised document like the I.E.E Wiring regulations(BS7671)

__________________
pnaban
Reply
Anonymous Poster
#10

Re: DG set selection

08/02/2010 10:02 AM

Gents;

I'm amazed at the response. Really a good attitude. Thanks, appreciate your time.

Rgds,

Prashant

Reply
Reply to Forum Thread 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); Humayun A Chaudhry (2); pnaban (2); Unredundant (2)

Previous in Forum: No Load Power consumption of different Induction Motors   Next in Forum: cable size

Advertisement