Existing System

08/03/2010 10:28 AM

I am doing a coordination study and found a switchgear assembly rated for 30kAIC 480Y277V 2000A and found the study to be able to deliver 95kA. The only solution I can begin to think of us Current limiting fuses sized at 1200A to series rate this system which will limit the fault to 30kA? Thoughts and ideas...

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Existing System

08/03/2010 11:36 AM

Are you sure of your numbers ? 95kA ? Well, you seem to be in North America, so it may not be far-fetched, with that very strong grid.

Fast acting fuses may do the job, but don't you need some discrimination ? Or cascading ? With fuses, any short-circuit may render the whole system dead, shutting off everything. Is that acceptable ?

Anyway, i am used to max 65kA systems here, and swithboards are built to that level of withstand, the incomer being an ACB of 65kA.

i look forward to answers from American experts on this subject, which will be some learning for both of us.

Cheers.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#2
In reply to #1

Re: Existing System

08/03/2010 2:06 PM

I wish I was wrong I have (4) 2500kVA 4160:480Y277V

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Existing System

08/03/2010 6:04 PM

check here

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: Existing System

08/03/2010 8:15 PM

There are two options here (I am guessing you are not replacing the existing switchgear assembly):

(1) Use current limiting (but time delay) fuse as you indicated

(2) Series inductance to reduce the short circuit current

The option (1) will be the simple and less expensive compared to the option (2).

I am not sure what leads you to select the 1200A fuse. For the case of selecting the current limiting fuse, do the study of the 'Peak Let-Through Curve' of the fuse and make sure it limits the short circuit current from 95kA down to below 30kA (25kA or less is preferred). You also have to be very careful for the device coordination as kvsridhar already indicated. If the current limiting fuse is selected appropriately, it will be blown only when there is a fault and it will occur before the breaker trips, so the system shutdown is not an issue. In the case of such fault, the system needs to be isolated anyway.

Documents in these links may help for the selection and coordination of current limiting fuse:

http://www.bussmann.com/library/docs/EPR_Booklet.pdf (see example in page 16)

http://www.littelfuse.com/data/en/Short_Circuit_Current_Ratings_Literature/PF992UsingFusestoIncreaseYourSCCR.pdf

http://us.ferrazshawmut.com/resources/media/articles/SC1-SelectiveCoordination.pdf

http://us.ferrazshawmut.com/resources/media/articles/TT.AFN2.pdf

In addition to limiting the short circuit current, it also helps to reduce the arc flash severity.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply