Residential Circuit Debug

08/06/2010 9:13 AM

I was gone for the day and on my arrival home, one circuit (on one breaker) in my home does not function. No outlets or lights work on the entire circuit. I have replaced the breaker (which does function to turn power on and off) and the GFCI (one in the circuit) with no change. I read voltage of 115 between hot-ground and neutral-ground. I am continueing to debug. Any advice?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Residential Circuit Debug

08/06/2010 9:23 AM

Press reset on the GFCI.

Reply
Anonymous Poster
#3
In reply to #1

Re: Residential Circuit Debug

08/06/2010 9:58 AM

I wish it was that easy. The test button won't trip the reset button which is why i thought the GFCI was broken.

Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#5
In reply to #3

Re: Residential Circuit Debug

08/07/2010 3:27 AM

Guest,

Usually testing for voltage from hot to ground in a GFCI will cause it to trip, for the same reason the 'Test' button trips it. Another clue that you have lost one of your connections or miswired the GFCI.

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Power-User

Join Date: Mar 2010
Posts: 105
#2

Re: Residential Circuit Debug

08/06/2010 9:26 AM

Sir,

Check for voltage in any socket with a Tester. If you find voltage ( Tester glows in both socket points) then it indicates broken neutral. Then you will voltage betweem N & E. Also check up the incoming neutral to the main board for your flat.

There may be a break in the earth line connected to the main earth .

Manroop.Chennai.

Reply Score 1 for Good Answer
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#4

Re: Residential Circuit Debug

08/07/2010 3:22 AM

Guest, First - welcome!

Second, From your terminology and descriptive details I must assume you are in the US.

Third, If you have not misstated your details, your biggest clue is being able to measure 115 volts from neutral to ground.

This should stand out to you as highly unusual since on your system they are supposed to be bonded together in a couple of specific places, keeping them quite close in potential. 115 volts is NOT quite close.

A tiny bit of deductive reasoning later and you have come to understand why I voted Manroop's answer a good one. Obviously your Neutral has lost its bond to your ground at some point between the GFCI and your breaker panel.

The next piece of your puzzle is what is the source of the 115 volts on the neutral?

In your system, you only have two possibilities; Line A or Line B, the 2 hot legs.

How does that potential get onto the neutral? Through a load or loads, to the point where all the neutrals are bundled together. Since the link from there back to the panel ground is loose, corroded, broken or otherwise compromised, you read the 115 volts to ground from there.

I usually look for a junction in a box where someone tried to put too many neutral wires in a wire-nut, or used a crimp style connector which has broken the wires up inside the crimp sleeve.

Think. Where have you recently made neutral connections? Check there first and save yourself a lot of time and frustration.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Commentator

Join Date: Jul 2010
Location: South Windsor, CT USA
Posts: 67
Good Answers: 2
#6

Re: Residential Circuit Debug

08/08/2010 11:04 PM

Is it possible you have a device on in the circuit and you read the voltage on the neutral through that device and lost the neutral as suggested earlier.

Reply
Reply to Forum Thread 6 comments