Bus Ways - Ampacity Rating

08/13/2010 3:42 AM

my superior and i are currently working with our 8 MW TG project...and we are going to try using BUS WAYS instead of using bare copper bus bars...now my problem is regarding its ampacity rating..i have an established full load ampere and conductor size if just using bare copper bus bars..how do we size up bus ways? how to check their ampacity ratings? im using a 1.0 A/ sq. mm current density in my calculation..

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Pathfinder Tags: bus way
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#2

Re: Bus Ways - Ampacity Rating

08/14/2010 1:51 AM

thanks for the threads...

now, do you know something of bus ways.???

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#3
In reply to #2

Re: Bus Ways - Ampacity Rating

08/14/2010 9:22 AM

bussways are conduits used to carry bussbars. Considerations in design and application ratings varies and are available from major manufacturers / suppliers. pls check this site for more info; http://www.fireengineering.com/index/articles/display/5703495882/articles/fire-engineering/construction-concerns/2010/06/cc-electrical-busways.html

__________________
vsar
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#5
In reply to #3

Re: Bus Ways - Ampacity Rating

08/18/2010 12:53 AM

clearly stated..you mean to say bus ways are only CONDUITS and not a conductor at all.??.cause i thought bus ways already contains copper conductors inside..i have here with me a catalogue of busways from a certain supplier...and it says that conductor is already embedded on it..im confused

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#7
In reply to #5

Re: Bus Ways - Ampacity Rating

08/18/2010 2:18 PM

Do not confuse bussways with waveguides used in microwave transmission applications! The appearance maybe the same but electrical characteristics are much different!

Bussways are not energy carrying devices themselves, but instead they are devices that serves as an insulated troughings for the current carrying conductors. Similar in purpose and applications to a conduit except for the shape and size which are normally governed by the size of the energy carrying bussbars.

__________________
vsar
Register to Reply
Anonymous Poster
#4

Re: Bus Ways - Ampacity Rating

08/15/2010 9:29 PM

The busbars size required for the busway is vary depends on the design of the overall product. You can refer to the IEC60439-2 standard for the Busway system

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#6
In reply to #4

Re: Bus Ways - Ampacity Rating

08/18/2010 12:57 AM

just browsed freeenginerring site...it seems my thought was correct..there is already conductors embedded inside..thanks a lot guys..

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Bus Ways - Ampacity Rating

08/18/2010 2:27 PM

Don't know where the idea came from that Busway had no conductors. Of course it does.

All you need to do is state the ampacity you want, don't get into calculating the cross sectional area, because each mfr is going to mount, insulate and space the bus bars inside in different ways, all of which will affect the cross sectional area they use to start with. But the one consistent thing between mfrs is the stated ampacity at the sated temperature and the stated resistance for use in calculating voltage drop. Here's really all you need concern yourself with from an application standpoint;

Ampacity.

Ambient.

Length, and associated acceptable VD if appropriate.

Orientation (Vertical or horizontal run).

Plug-in devices, if any.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#9
In reply to #8

Re: Bus Ways - Ampacity Rating

08/18/2010 10:00 PM

thanks a lot JRaef...my heads all cleared now with the sizing-up of busways..another concern i have here is regarding its ratings..is it in per phase or of line-to-line value.??

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10

Re: Bus Ways - Ampacity Rating

10/02/2010 8:28 AM

The recommended solution is to write to a manufacturer

__________________
pnaban
Register to Reply