Use of 60 Hertz Frequency in the USA

08/13/2010 10:38 AM

dear sir myself ruchir want to know why use of 60 hertz frequency in usa is done for electric power generation

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: use of 60 hertz frequency in usa

08/13/2010 10:43 AM
__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Use of 60 Hertz Frequency in the USA

08/13/2010 11:56 AM

From a standpoint of "cycles per second", and that with 60cps there are 360 rotations in a minute and 360 degrees in a circle, and rotation is a function of a circular movement, or Revolutions, which is measured in Revolutions per Minute, 60cps seems fairly logical and simple to me.

So the real question is, what possessed AEG to decide NOT to use 60cps? Seems to me to have been some sort of mathematical elitist decision based on 60 not being a "preferred number". Sure, 50 goes into 100 easier, but where does anyone use the number 100 when discussing rotation?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#4
In reply to #2

Re: Use of 60 Hertz Frequency in the USA

08/13/2010 8:24 PM

Didn't we just do this? In the early 1900s as motors were becoming widespread, power converters were difficult to synchronize at high frequencies, i.e., above 40 Hz. Westinghouse gambled on being able to use 60 Hz (and tesla really liked 60 as a number) while AEG took the safer bet. Both gave decent flicker smoothing.

1500 RPM gives 50 Hz nicely. 1800 RPM gives 60 Hz nicely.

Herman Westinghouse thought it should be 133 and some change, but he couldn't get anything to go that fast.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Anonymous Poster
#3

Re: Use of 60 Hertz Frequency in the USA

08/13/2010 12:08 PM

As I've said before, I'll be willing to bet that some how, some way the selection of 50/60Hz involved an engineer trying to impress a woman.

"Sure, baby...over in France the electricty is 50Hz. But me? I generate at 60Hz. 10 whole Hz stronger. Yeah, I'm kind of a rebel."

*swoon*

Register to Reply Score 2 for Off Topic
Anonymous Poster
#5

Re: Use of 60 Hertz Frequency in the USA

08/13/2010 11:03 PM

Europe's got 50hz

we got 60hz for the same money

it's all about economics

Register to Reply
Power-User

Join Date: Jul 2010
Location: Near ... New Orleans, Louisiana, USA
Posts: 217
Good Answers: 3
#6

Re: Use of 60 Hertz Frequency in the USA

08/14/2010 1:46 AM

Economics, I'm sure is involved. If I remember correctly, the higher frequencies don't require as large a transformer or motor. Yet the higher the frequency, the harder it is to transmit long distances. So I guess a compromise between the 2 that gives the sensation of no flickering was what they chose.

Look at your computer monitor ... what is the frequency of the monitor. I'd suggest that there is a frequency below which you get eye strain ... Old films were in the 40 frames per second ... and they flickered a bit. But the scenes changed so often that you weren't bothered (much). TV broadcast in color in the NTSC did not turn out too well in Europe. They would up creating a different system (PAL) ... which was better ... at least for the color but slower for the refresh rate. Again, no biggie because the scenes changed so frequently. But why do we now have TV's now with 120hz and more? Because it looks better, you see fast motion clearer.

Incandescent light bulbs flicker too. Think of your incandescent light bulb as a strobe light, that flashes 5 to 6 times faster.

Have you checked your monitor yet ... mine is at 70hz ... I notice a difference at 60 after a hour or so.

I can remember when the first color monitors came out that bragged about 48hz and the headaches. Some people are more sensitive than others I guess. TV is not as bad because the screen changes so frequently ... but on a monitor, there is usually a background that is just a-flickering away at you.

Economics and the flicker ... and what you were willing to compromise on, is my final answer Regis.

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#7
In reply to #6

Re: Use of 60 Hertz Frequency in the USA

08/14/2010 7:04 AM

"Incandescent light bulbs flicker too" - true, to a very small extent. Generally the flicker in light output from an incandescent lamp can only be detected by measurement with pretty sensitive instruments, even at 50Hz (due to the thermal time constant of the filament).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 2 for Off Topic
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#8
In reply to #7

Re: Use of 60 Hertz Frequency in the USA

08/14/2010 7:36 AM

Why, oh why, is one of the few factual statements on this marked "off-topic"?

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply Off Topic (Score 5)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#9

Re: Use of 60 Hertz Frequency in the USA

08/14/2010 12:40 PM

There isn't any point worrying about 50/60Hz. We will eventually return to DC power for all our home use and distribution.

Almost all the loads around the house are DC as they use an AC to DC power supply. Even the motors in appliances are being switched to various brushless DC controllers.

The distribution with DC is becoming a reality for large networks and could be brought closer to home in the next 20 years. The pole mounted AC transformers will be replaced by DC/DC converters. The power electronics is getting there. The safety problems of DC power distribution will be solved with the solid state switches and protections acting in the uS range. The intelligent grid will be a step in this direction as more monitoring and controls will be needed.

Most alternative energies are better at producing DC than AC. Solar panel, variable speed wind mills, thermal converters...

DC power should improve the system efficiency bu reducing the skin effect and transformer core losses. Hopefully this gain will be larger than the power electronics conduction and switching losses.

Energy storage for home and cars is mostly DC in batteries. A DC network should simplify the energy conversion. DC only electrical supply is increasingly used in "off grid" installations.

Eventually, AC power distribution will become the exception. But not tomorrow. This is introduced in specific applications and will spread if real merits are found.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#10
In reply to #9

Re: Use of 60 Hertz Frequency in the USA

08/14/2010 5:50 PM

What range of DC voltages are you envisaging for distribution?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#11
In reply to #10

Re: Use of 60 Hertz Frequency in the USA

08/15/2010 12:52 PM

It is likely that similar voltages as used for the AC will be used. There will be some differences but not that much as the already installed cables can carry only a little more power in DC than in AC. The insulation might have to be derated for DC applications. We only want to replace the transformers, not all the distribution network. Residential areas will have about 10-12KV lines stepped down to the usual 110 / 220 volts or maybe lower in order to keep the same wiring and distribution in the houses.

We might even have multiple voltages available in the houses. Most plugs would be low voltage for the small loads, computers, TV, LED lighting... The electric and microwave ovens would need hundreds of volts to get the power with reasonable wire size. The exact voltage might even vary over a larger range than with the present AC network. The power converters in each load already have the ability to regulate over a 2:1 range.

High voltage line between cities and production centers will be in the many hundreds of KV as already exist in large DC links. We won't need to have power factor compensation stations along the line or in the factories. Harmonics will also be a thing of the past, replaced by switching noise issues...

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#12
In reply to #11

Re: Use of 60 Hertz Frequency in the USA

08/15/2010 4:41 PM

I know bugger-all about this, but I'm struggling with the step-down from >100kVDC to about 100VDC. How easy/reliable is it? Can it be done in one stage?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#13
In reply to #12

Re: Use of 60 Hertz Frequency in the USA

08/15/2010 5:05 PM

Assuming that this gets done some day.

Similar to the current distribution system, the 200-500KV from the generation station will be reduced to about 10KV for residential transport. There might even be steps in between.

The DC system will allow parallel connection of distribution lines and redundancies that are not possible today.

The 10KV will then be reduced to ~100 to 200V for home usage.

This is presently done by 60Hz transformers. It will be done with high frequency transformers that are much smaller. The semiconductors used will probably be silicon carbide or industrial diamonds instead of plain silicon.

Today, it is difficult to produce a transistor handling more than 3KV. Eventually, the new switches will handle many times this voltage. This will make the DC distribution possible at a reasonable price. We already do some of it now but it is too expensive to use at large.

It is very likely that the drive for DC power distribution will come from the users and possibly in emerging countries where they will be starting with a blank page. Or after the third world war when we will have to rebuild the infrastructure...

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#14
In reply to #13

Re: Use of 60 Hertz Frequency in the USA

08/15/2010 5:28 PM

OK, cheers. I look forward to the day. I thought you were talking about technology that was already (economically) available. .

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); JohnDG (5); JRaef (1); marcot (3); one2playwitt (1); TVP45 (2)

Previous in Forum: Transformer VA Distribution   Next in Forum: Reactive Power Capability

Advertisement