How much AC power needed to meet DC Load

08/14/2010 11:48 AM

Dear sir

I have a constant load of 100KW,48V DC. Load is inductive.

suggest good rectifier and filter circuits.

My doubt is How much AC power needed to meet this constant load.

Suppose if load is varying 25% extra,then how much AC power we can expect.

Kindly give ur advice in this topic.

Regards

gova

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: How much AC power needed to meet DC Load

08/14/2010 1:12 PM

Good question, I am also waiting who will response.

Register to Reply
Associate
Pakistan - Member - New Member

Join Date: Dec 2009
Posts: 29
#2

Re: How much AC power needed to meet DC Load

08/14/2010 5:25 PM

Dear All,

  • For 100KW @ 48VDC you need 2084amp.

For Transformer (480VAC) your need 1733.888KVA = 1750KVA

  • For 125KW @48VDC it is 2605amp.

For Transformer (480VAC) your need 2167.36KVA = 2200KVA

For More Please see bellow mention Literature.

Short Circuit Capacity: Basic Calculations and Transformer Sizing

Short circuit capacity calculation is used for many applications: sizing of transformers,
selecting the interrupting capacity ratings of circuit breakers and fuses, determining if a
line reactor is required for use with a variable frequency drive, etc.

The purpose of the presentation is to gain a basic understanding of short circuit capacity.
The application example utilizes transformer sizing for motor loads.

Conductor impedances and their associated voltage drop are ignored not only to present a
simplified illustration, but also to provide a method of approximation by which a plant
engineer, electrician or production manager will be able to either evaluate a new application
or review an existing application problem and resolve the matter quickly.

Literature containing a detailed discussion of short circuit capacity calculations are
available within the electrical power transmission industry. [1]

The following calculations will determine the extra kVA capacity required for a three
phase transformer that is used to feed a single three phase motor that is started with
full voltage applied to its terminals, or, "across-the-line."

Two transformers will be discussed, the first having an unlimited short circuit kVA
capacity available at its primary terminals, and the second having a much lower input
short circuit capacity available.

kVA of a single phase transformer = V x A

kVA of a three phase transformer = V x A x 1.732, where 1.732 = the square root of 3.
The square root of 3 is introduced for the reason that, in a three phase system,
the phases are 120 degrees apart and, therefore, can not be added arithmetically.
They will add algebraically.


Transformer Connected To Utility Power Line

The first transformer is rated 1000 kVA, 480 secondary volts, 5.75% impedance.
Rated full load amp output of the transformer is


1000 kVA / (480 x 1.732) = 1203 amps


The 5.75% impedance rating indicates that 1203 amps will flow in the secondary if
the secondary is short circuited line to line and the primary voltage is raised from
zero volts to a point at which 5.75% of 480 volts, or, 27.6 volts, appears at the
secondary terminals. Therefore, the impedance (Z) of the transformer secondary may
now be calculated:


Z = V / I = 27.6 volts / 1203 amps = .02294 ohms


The transformer is connected directly to the utility power lines which we will
assume are capable of supplying the transformer with an unlimited short circuit
kVA capacity. The utility company will always determine and advise of the short
circuit capacity available at any facility upon request.

With unlimited short circuit kVA available from the utility, the short circuit
amperage capacity which the transformer can deliver from its secondary is


480 volts / .02294 = 20,924 amps


An alternative method of calculating short circuit capacity for the above
transformer is:


1203 amps x 100 / 5.75% = 1203 / .0575 = 20,922 amps


Another alternative is to consult a reference manual. Cutler- Hammer Consulting
Application Catalog, 12th Edition, gives the specifications for the above mentioned
transformer and the value of the short circuit capacity in Table A25 on page A-59.
The short circuit capacity is given as 20,900 amps.

Now we are ready to apply a motor to the terminals of the transformer secondary.
We must determine the voltage drop which will be caused by the motor inrush on
start. If the voltage remains within the rated voltage of the motor, then no oversizing
of the transformer is required.

Motors rated for 460 volts are for use with distribution systems that are rated at
480 volts. The rating system allows a twenty volt drop in the distribution system
which may occur along the feeder cables which connect the power transformer to
the load. The NEMA specification for a standard motor is that it requires the motor to
be capable of operating at plus or minus 10% of nameplate voltage. Therefore, the
voltage drop on inrush should not be allowed to drop below 460 volts less 10%,
or, 414 volts.

The transformer will be asked to supply power to a motor which has a full load amp
rating of 1203 amps, which will fully load the transformer. Therefore, we will rate
the motor at 460 V x 1203 A x 1.732, or, 958.5 kVA. We will assume that our motor
will have an inrush of 600% of its full load rating which will cause an inrush of


460 V x 1203 A x 600% x 1.732 = 5751 kVA


The voltage drop at the transformer terminals will be proportional to the motor load.
The voltage drop will be expressed as a percentage of the inrush motor load compared
to the maximum capability of the transformer. [2] The transformer has a maximum kVA
capacity at its short circuit capability, which is


480 V x 20,924 A x 1.732 = 17,395 kVA


The voltage drop on motor inrush will be


5751 kVA / 17,395 kVA = .331, or, 33.1%


The transformer output voltage will drop to 480 x .669, or, 321 volts. Thus, we can
see that the transformer is much too small to use a motor that has a full load rating
equal to the full load capacity of the transformer.

The transformer must be sized so that its short circuit capabilty is equal to or
greater than 5751 kVA times 10, or, 57,510 kVA in order to have a voltage drop of 10%
or less. Therefore, the short circuit amperage capacity of the transformer to be used
must be a minimum of


57,510 kVA / (480 V x 1.732) = 69176 amps


A typical 2500 kVA, 5.75% impedance transformer will have a short circuit capacity of
52,300 amps. The next highest standard size transformer at 3750 kVA will have a 6.5%
impedance and would have a short circuit output capability of 69,395 amps which will be
sufficient.

In the particular application discussed, the ratio of the selected standard size
transformer kVA to motor kVA is 3750 kVA / 958.5 kVA = 3.91. Thus the transformer
rating is 391% larger, or, nearly four times, the rating of the motor. Note the non-linear
effect of the impedance rating of the transformers on their short circuit capacities.


Transformer Connected To An Upstream Transformer

The second transformer we will examine will have a finite short circuit capacity
available at its primary rather than an unlimited capacity. We will assume that a facility
derives its power from the same 1000 kVA transformer mentioned above and that the
second transformer is connected directly to the terminals of the 1000 kVA transformer.
Thus, feeder cables between the two transformers are eliminated and the impedance of
cables are not taken into account. However, the smaller the motor leads, the less will be
both the short circuit capacity and the voltage delivered to the motor terminals.

The second transformer, which will have a 480 volt primary and a 480 volt secondary, will
be used to power a 20 HP, 3 phase, 460 volt motor which will be started at full voltage. The
motor will be the only load on the transformer.

Sales catalogs by various manufacturers will invariably recommend a "minimum
transformer kVA" of 21.6 for use with a 20 HP motor. The minimum transformer kVA ratings
are for use with multiple motors on a single transformer. A multiple motor configuration
will be discussed in the next section of this article.

The 21.6 kVA is calculated as follows:


480 volts x 26 nominal amps x 1.732 = 21.6 kVA


The transformer manufacturers will give a 20 HP motor a nominal full load amp rating
of 27 amps, thus allowing no extra capacity:


460 volts x 27 nominal amps x 1.732 = 21.5 kVA


One motor manufacturer has rated a 20 HP motor at 26 Full Load Amps, 460 VAC,
205 Locked Rotor Amps, 81% Power Factor. The motor will present a load of


460 volts x 26 amps x 1.732 = 20.7 kVA


The starting motor kVA load with inrush current will be


460 V x 205 A x 1.732 = 163.3 kVA


We will consider using a 30 kVA general purpose transformer to supply the 20 HP motor.
The transformer will have a nominal impedance of 2.7% and an ouptut of 36.1 amps at
480 volts. The short circuit current capacity that can be delivered to the 21.6 kVA
transformer by the upstream 1000 kVA transformer is 20,924 amps, or, 17,395 kVA.

The short circuit amperage capacity of a transfomer with a limited system short circuit
capacity available at its primary is:


transformer full load amps / (transformer impedance + upstream system impedance as seen
by the transformer)


Where:


upstream system impedance as seen by the transformer =
transformer kVA / available primary short circuit capacity kVA


Therefore,


36.1 amps / [2.7% + (30 kVA / 17,395 kVA)] =
36.1 / (2.7% + .0017%) = 36.1 / .0287 = 1258 short circuit amps


The transformer output voltage drop upon motor inrush will be:


motor inrush kVA / short circuit kVA =
163.3 kVA / (480 V x 1258 A x 1.732) = 163.3 kVA / 1046 kVA =
.156 = 15.6 %


A 30 kVA transformer rating is too small as the motor voltage drop will exceed 10%.

A 45 kVA transformer with a 2.4% impedance and an output of 54.1 amps at 480 volts
would have a short circuit capacity of 2034 amps. The voltage drop upon motor inrush
would be 9.66%.

For a single motor and transformer combination, one transformer manufacturer
recommends that the motor full load running current not exceed 65% of the transformer
full load amp rating. [3] Thus, for our 26 amp motor the transformer rating should be
a minimum of 40 amps, or, 33.3 kVA.


Multiple Motors On A Single Transformer

The minimum transformer kVA is given by transformer manufacturers so that a transformer
may be sized properly for multiple motors. If there are five motors on one transformer, add
the minimum kVA ratings and then add transformer capacity as necessary to accomodate the
inrush current of the largest motor.

The transformer thusly selected will be capable of running and starting all five motors
provided that only one motor is started at any one time. Additional capacity will be required
for motors starting simultaneously.

Also, if any motor is started more than once per hour, add 20% to that motor's minimum
kVA rating to compensate for heat losses within the transformer.


Motor Contribution to Short Circuit Capacity

When a fault condition occurs, power system voltage will drop dramatically. All motors
that are running at that time will not be able to sustain their running speed. As those motors
slow in speed, the stored energy within their fields will be discharged into the power line.
The nominal discharge of a motor will contribute to the fault a current equal to up to four
times its full load current.

With our 1000 kVA, 1203 amp transformer example given above, we will assume that all
1203 amps of load are from motors. The actual short circuit current will equal 20,924 amps
plus 400% of 1203 amps for a total of 25,736 short circuit amps.

When sizing the transformer for motor loads, the fault current contribution from the
motors will not be a consideration for sizing. However, the motor contribution must be
considered when sizing all branch circuit fuses and circuit breakers. The interrupting
capacity ratings of those devices must equal or exceed the total short circuit capacity

available at the point of application.

Regard's

__________________
AUR
Register to Reply Off Topic (Score 3)
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Aug 2006
Location: Midwestern United States
Posts: 843
Good Answers: 76
#8
In reply to #2

Re: How much AC power needed to meet DC Load

08/16/2010 3:10 PM

Quote: "For More Please see bellow mention Literature."

Thank you for providing a hint that the majority of your information was garnered form another source. Please know that when copying someone else's work in its entirety, it is proper etiquette to provided specific information related to 'from whom' and 'where' the information was garnered. For example...


http://www.powerqualityanddrives.com/short_circuit_transformer/

Copyright © 2001 Francis J. Martino

Otherwise you are very close to plagiarism and partaking in copyright infringement. In fact, you shouldn't 'copy' copyrighted material anyway, kind of the whole point of the copyright. It would be best in the future just to provide a link to the source.

JavaHead

__________________
Reuters - Investigators found that the recent thread derailment in CR4 was caused by over-weight creatures of lore and request that membership DON'T FEED THE TROLLS.
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#3

Re: How much AC power needed to meet DC Load

08/14/2010 6:25 PM

how can a DC load be inductive is a better question..

__________________
jinxnao
Register to Reply Score 1 for Good Answer
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: How much AC power needed to meet DC Load

08/14/2010 7:46 PM

"My doubt is How much AC power needed to meet this constant load."

Power is power is power, it knows not from whence it came. AC, DC, fossil fuels, it's still power. So if you have a 100kW DC load, it will consume 100kW from the AC system, plus any transformation / conversion losses. So until you define how you are getting from AC to DC, you cannot define the total power consumption from the AC side.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Member

Join Date: Aug 2010
Posts: 6
#5

Re: How much AC power needed to meet DC Load

08/14/2010 11:29 PM

30 amps 240 Volt

Register to Reply Score 2 for Off Topic
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7
In reply to #5

Re: How much AC power needed to meet DC Load

08/15/2010 4:16 PM

Please re-read the original post as the load is 100kW = 100,000W

__________________
jack of all trades
Register to Reply Off Topic (Score 5)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6

Re: How much AC power needed to meet DC Load

08/15/2010 4:13 PM

There is not enough information provided to safely answer this question. I am assuming you are talking about a three phase ac supply + three phase bridge rectifier + filtering capacitor bank to power a 100kW 48V DC load (galvanising plant perhaps?). Without knowing what the load is we cannot specify the level of DC filtering.

Please provide more information including the application and what the load actually is.

Given the information so far I would have to suggest you get an engineer and/or electrician in to help design and build the power supply system for you as the voltages, currents and potential capacitor energy storage levels are at dangerous potentials - both to any staff working on the equipment and to the equipment and plant itself if this is done incorrectly.

__________________
jack of all trades
Register to Reply Score 2 for Off Topic
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".